So could you give me an example of how it will become live and stay live. And not eg with T+E on tray!

I really can't be arsed, but your assuming that only cables using an earth sheath are ever going to be installed onto any cable tray or basket that's been fitted. Personally i wouldn't install T&E cables on either system, but there are plenty here that would, and see no problem with it either. So you can't ask to leave T&E out, or say flexible cables and the like!! If a cable tray/basket system has been installed, then it's undoubtedly going to be used by others in the future. Earth it and be done with it, rather than arguing to the contrary!!
 
evrey piece of tray should have it's own earth rod into the ground, at least 10' deep, with the connection enclosed in a propriety earth pit, rod to be encased in bentonite and have a Ra of not more than 21ohms. connection cable to said earth rod to be deemed a minimum of 10mm.
 
An earlier post mentions damage from cranes. Why would anyone install any type of containment were its likely to get bashed on a regular occurrence?
 
An earlier post mentions damage from cranes. Why would anyone install any type of containment were its likely to get bashed on a regular occurrence?

anywhere within 3 miles of a FORK LIFT TRUCK DRIVER IS A DANGER ZONE.
 
An earlier post mentions damage from cranes. Why would anyone install any type of containment were its likely to get bashed on a regular occurrence?

That was me mate and if you've misread my post or I haven't explained properly then I shall explain:)

We have 3 overhead cranes which are used for lifting humongous hoses/structures/metal bars etc etc etc.
The said tray does not get bashed on a regular basis at all (where did you read that?)but it is in the firing line in various places due to a constant re-arranging of the 'work flow' in the factory and some hamfisted operators.
My point was that it is possible/not probable for this to be hit and damage a cable which 'could' make the tray 'live' hence one of the reasons I earth my tray.............phew.
Hope that has cleared your misunderstanding up :)

"Lots of hand-fisted fitters here with cranes swinging stuff all over the place"
"Damage to cables caused by equipment hitting it with the overhead cranes.............not probable but could and nearly has happened".
 
Last edited by a moderator:
Ok lads put your guns away i'm not saying your right or wrong!
The tray/basket is not at fault here its how its used.

Eng I love the way you bond all tray/basket but when someone says there going to run a cpc in metal conduit on here you jump on them like a pack of wolves.(if my memory serves me correct)

"SWA, MI run on tray" earth or bond whats the point.
"Tray work connected to earth and then enters the building" bond within 600mm on entering.
IMO "T+E on tray" earth and treat as cpc like metal trunking/conduit

So what would be the point of earthing conduit/trunking, if your daft enough to pull separate CPC into them!! Which is the point i was making above!!
The point i'm making as far as tray and baskets installations, is why wouldn't you earth them from the panel/DB they originate from?? As far as i'm concerned, ...None!!
 
Cleaner comes into room, plugs hoover into socket but "cunningly" throws cable for hoover over unearthed cable tray in order to make her life easier.

She does this for months and months and cable not surprisingly exposes bare copper.

This copper happens to be at 230v (actually 240v as it was a while ago :) ) and whole tray carrying networking cables also becomes live and gives the network guy a nasty zap when he comes along to do some "server stuff".

I was the network guy.

You can never predict what the stupid do and in my opinion, for the sake of some cable and time, plan that way.

Good enough for you :p :)

EDIT:- Appreciate there were multiple failings that contributed to this, but you get the jist.

Go on then give us all an example.
 