Hello all,
Just after some guidance, i am a qualified Auto Electrician with a good number of years behind me. While confident in my own ability in domestic applications i am not fully aware of the Regs.

I am planning on installing 3 or 4 (mind not made up yet) brick lights in my garden wall parallel with my drive.

I intend on running 1.5mm SWA along the wall clipped with SWA cleats which will be circa 400mm above the level of the soil in the garden looping in and out of wiska Junction Boxes with the correct earthed glands etc.

The question is am i then OK to run flex (maybe pond flex) from the junction box through the wall to the back of the brick light. The wall is 2 bricks thick (double thickness) i will use the correct glad on the flex.
(The picture below shows the lay out if it uploads ok.) Credit Google image search

Thank you
James.
search


j box.jpg
 
can't see a problem with your suggested method. bear in mind the circuit needs to be RCD protected (18th Ed.), so be wary of possible water ingress. ( unless of course, you designed it pre Jan. 1st. 2019.o_Oo_Oo_O.)
 
Super thank you very much.
That has confirmed my thoughts on the matter.

The feed for these lights is from a spare 6A RCD in the house consumer unit.
Up to a switch in the cupboard under the stairs.
Back down under the under drawing in to a junction box, at this point it will change from 1.5mm T&E to the 1.5mm SWA. secured with the relevant cable clips/cleats.
Pass out through the house wall to the outside under the flagging in conduit before emerging at the garden wall.
 
If they are on a rcbo or rcd of themselves that would be better as it is prone to tripping due to water ingress. this would prevent half your house tripping aswell unnecessarily
 
Hello all,
Just after some guidance, i am a qualified Auto Electrician with a good number of years behind me. While confident in my own ability in domestic applications i am not fully aware of the Regs.

I am planning on installing 3 or 4 (mind not made up yet) brick lights in my garden wall parallel with my drive.

I intend on running 1.5mm SWA along the wall clipped with SWA cleats which will be circa 400mm above the level of the soil in the garden looping in and out of wiska Junction Boxes with the correct earthed glands etc.

The question is am i then OK to run flex (maybe pond flex) from the junction box through the wall to the back of the brick light. The wall is 2 bricks thick (double thickness) i will use the correct glad on the flex.
(The picture below shows the lay out if it uploads ok.) Credit Google image search

Thank you
James.
search


View attachment 47328
Your picture doesn't make it clear if the 'banjo' has been used in the SWA terminations. It will be needed in order to earth the armour.
Edit.. Actually your picture couldn't make it more clear that you have earthed them so please ignore the above!:oops:
 
Thank you for your advice,
Yes the lights will be on there own 6A RDC as i have a spare in the house Consumer Unit, so will utilise this for the proposed outside brick lights, I do have 3 outside wall lights (2 LED Floods on PIR and one Dawn till Dusk these or at least the wiring were already there when i moved in, these are on one of the existing 6A lighting rings.)

I am intending on using 1.5mm² 3 core SWA so will obviously use the earth core and earth the SWA armour through the banjo fittings, as shown in the image. Is soldering them acceptable as shown? i had the understanding that solder was not used on domestic / 240v applications.

As long as everyone agrees that i am ok to run the lamp feed from the wiska junction box to the light with pond flex or a simular cable, as it will only have a very small amount exposed between the junction box and were the flex disappears in to the wall then i am happy :)
 
Hi - You've done a nice job of soldering :) .
If I was doing this I'd lash out on a second nut on the inside so the banjo is locked between them. It turns out the plastic has been known to creep away over time and the pressure comes off the connection.
 
i would advise buying one of these :https://www.NoLinkingToThis/p/earthing-nut-20mm-pack-of-2/77809
one end of the earth cable coming from the swa then has to be crimped into an o - shaped crimp
the crimped end is then screwed into the earthing nut and the other goes to the earth terminal.
this saves soldering and time and is also a very secure connection.
 
I would bury the cables and adaptable boxes in the ground and just run the flex up the wall.
Fill the adaptable boxes with a gel to prevent moisture ingress.
SWA glands should be the CW type.
 
The earthing nuts look like a good idea. And also act as a lock nut. I’d make a small earthing strap with a crimped ring connector to run from the banjo screw to the Earth terminal block, and attach the earth cable in the sea to the nut also with a crimped ring connector.I’m happy to solder as it’s something I’d done a lot of over the years,but would be more of a fiddle when working in the garden over soil.

With regards to burying the cable this would be a neater option. Am I ok with regards to the Regulations to then run the flex up out of the soil and in to the wall. I thought a 240v cable would have to be armoured if any of it was underground, I apologise if I seem like I’m doubting you as I’m really not. I just want to make sure it’s all safe and in accordance. :)
 
The earthing nuts look like a good idea. And also act as a lock nut. I’d make a small earthing strap with a crimped ring connector to run from the banjo screw to the Earth terminal block, and attach the earth cable in the sea to the nut also with a crimped ring connector.I’m happy to solder as it’s something I’d done a lot of over the years,but would be more of a fiddle when working in the garden over soil.

With regards to burying the cable this would be a neater option. Am I ok with regards to the Regulations to then run the flex up out of the soil and in to the wall. I thought a 240v cable would have to be armoured if any of it was underground, I apologise if I seem like I’m doubting you as I’m really not. I just want to make sure it’s all safe and in accordance. :)
Yes the flex should be in some flexible conduit, while it’s under the ground.
 
Just to pick up on one quick thing.... Is the circuit RCD protected? You mention its on its own 6A RCD but you probably mean MCB, just check if its an RCBO then all is well, or if its an MCB then its on a section of the board with an 30mA RCanin front of it
 
Sorry Yes you are correct its on it will be on its own 6A MCB not RCD i get confused between the two.
I will check tonight if its an RCBO type or if it has a 30mA RCA in front of it.
I might upload a picture for you kind people to help me.
 
Hi guys I’ve just checked and it looks like it does have a 30mA RCD in front of the 6A mcb. So I should be all good :)

89EB05F6-24CC-461B-ACFB-66FBD74FA4CF.jpeg

7CB1FED2-2483-49F2-BE82-EDBEAEB63333.jpeg
 
@DefyG ,

Is this a genuine dumb or a slip of the finger/thumb whilst scrolling the page?

upload_2019-2-11_14-3-57.png

I'm curious because if what I've suggested is a dumb idea I'd like to know why so I can adjust my thinking maybe :)
 

Reply to Brick Lights. SWA terminating. in the DIY Electrical Advice area at ElectriciansForums.net

Similar Threads

I'm looking at putting up & down lights onto a solid brick wall (1900 semi detached house) What's best way practically and aesthetically to...
Replies
15
Views
2K
For various reasons out of my control, we have wound up in a situation where we have 1.5mm SWA cables buried in these pillars and exiting out of...
Replies
95
Views
7K
I am adding a light fixture in a room I am restoring in my 160 yo house. I have ran a new 12-2 w/ground wire from the ceiling box to a junction...
Replies
2
Views
850
Good Afternoon All Currently doing an EICR on common parts of a big site with multiple blocks. All blocks have outside garden spike lighting in...
Replies
11
Views
487
Howdy DIY soldiers, first post here. My question comes down to whether it would be particularly unsafe for me to temporarily wire nut and tape a...
Replies
2
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock