Does seen very cheap, even for London, something doesn't sound right with it though, what else will they "find" when carrying out the work. What will be feeding the new rcd units, I'm guessing that they will just be off the ring again?
this is what it will be Chris...
its the charlie browns of the electrical world....
 
Think we have had a post like this plenty times before BG are owned by a private equity company who in my view a pure sales driven and I don't just say this to bump my gums I have discussed with with a few ex BG guys who were driven from their job because the were being pressured to put sales first .

One guy came to service my boiler under a BG contract he was a contractor to BG yet worked for them for 28 years before chucking it only to be offered a subbies job from them now he does 3 days a week and as he put it the monkey is off his back
 
Just done an inspection for a customer who had BG in to sort a tripping breaker took them 3 days couldn't sort it told customer would have to chase out walls and replace cable but they weren't covered to carry out the chasing need to get a builder into do it
10 minutes to sort it out they had the following all off 16a mcb on 3 separate radials
Dishwasher ,kettle ,tumble dryer , washing machine and power shower pump but a spare 20a radial with just an outside socket on it so split the load solved problem no wall chasing

thats so stupid theres nothing i can do other than point and laff , like this.........