Hi all

Just checked job and 6mm live supply is burnt out on 8.5kw shower. Run is 4 metres clipped direct with no insulation my calcs are that this should be perfectly fine. Was also on a 40 amp wylex push type mcb. Terminations seemed fine. Has anyone got any possibilities what may be causing this? I was also getting 115v across disconnected live feed and load neutral. My understanding is that this can be normal but can someone clear up the theory behind this. Thanks
 
115V measured with what? What exactly was disconnected and where?

As above, normally the damage is caused by heat conducted from high-resistance terminations or contacts. Was there any damage to the cable that was more than a foot away from the ends?
 
Are you saying the entire cable has burnt out or just at a termination?
It's very common for shower/switch terminations to burn out due to poor connections.

It was about an inch up from termination radiohead. Thing that makes me bit more dubious though is that shower has recently gone in to replace a previous faulty one and that customer reported that shower would seems to alter temperature quite extremely even when using same temp setting on dial. I suppose this could perhaps still be down to the loose connections on pull cord if voltage and current being affected by the loose connection
[automerge]1594756850[/automerge]
115V measured with what? What exactly was disconnected and where?

As above, normally the damage is caused by heat conducted from high-resistance terminations or contacts. Was there any damage to the cable that was more than a foot away from the ends?
Hi Lucien

115v was measured between disconnected live supply at pull switch and the still terminated load neutral to shower. The signs of burnout were only about an inch up from termination. As post above though do you think that this loose connection could have been affecting the dramatic changes in water temperature that customer reported
 
Yes, absolutely. The terminal was probably arcing causing the voltage to fluctuate at the shower and heating the cable instead of the customer.

Still not sure what was disconnected; was the line cable disconnected at the CU, or disconnected from the switch but still live, or what?
 
Yes, absolutely. The terminal was probably arcing causing the voltage to fluctuate at the shower and heating the cable instead of the customer.

Still not sure what was disconnected; was the line cable disconnected at the CU, or disconnected from the switch but still live, or what?
Live at switch I think he means?....? or I hope he does ??
 
If the cable was been overloaded to the point it burnt out the line conductor in the pull switch I would expect to see some kind of thermal damage at all the MCB aswell? Worse case is it’s pulling 37 amps, so should be more than suitable.
 
Live at switch I think he means?....? or I hope he does ??
Live at switch I think he means?....? or I hope he does ??
lol I am mate
[automerge]1594758209[/automerge]
Yes, absolutely. The terminal was probably arcing causing the voltage to fluctuate at the shower and heating the cable instead of the customer.

Still not sure what was disconnected; was the line cable disconnected at the CU, or disconnected from the switch but still live, or what?
Thanks for confirmation Lucien. The line just disconnected at switch and tested across this the still connected load neutral
[automerge]1594758329[/automerge]
If the cable was been overloaded to the point it burnt out the line conductor in the pull switch I would expect to see some kind of thermal damage at all the MCB aswell? Worse case is it’s pulling 37 amps, so should be more than suitable.
Thanks Chris that's what my calcs came out with so no concerns about cable size and yes signs of thermal damage at MCB
 
Last edited:

Reply to Burnt out 6mm on 8.5kw shower in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello, I'm not an electrician, more one of those 'competent DIYers', so probably the worst kind :) My electric shower broke, the shower firm came...
Replies
13
Views
1K
Hi everyone. Hopefully someone can help with a little mystery i had today. The issue is fixed but I want to understand what was going on to help...
Replies
8
Views
561
Hi We recently had an 7kW EV charger installed. Due to the consumer unit being situation within the kitchen of our bungalow, the cable needed to...
Replies
10
Views
4K
I own a top floor tenement flat that I used to live in and then rented out after I married. It is currently empty whilst some work is being done...
Replies
0
Views
142
Hi all, Was wondering if anyone has come across this before and could maybe help - Its a new one to me! Customer recently altered layout of...
Replies
7
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock