Very true.The volt drop calculations are sometimes impractical. Working on industrial sites the final circuit might be connected to a sub-sub-sub-submain 400m away. The design data is normally lost or a water damaged scroll that only one operative knows of and the addition and alterations somewhere else or not recorded. I doubt theres any % left on a lot of these sites.
If you measure the end of circuit PSCC and divide by 20 then you get the current for which it meets 5% VD. E.g. Measure 350A PSCC then 5% drop overall met for 17.5A.
Why? Well the PSCC is what flows at 100% voltage drop!
You don't have to meet overall 5% drop in the regs as such, as the DNO side is supposed to size the supply and voltage so under load you are within the limits, and on high current circuits it may not be practical at all as the DNO side drop could well exceed 5%, but the above is a quirk sanity check of the system when other aspects are hidden, undocumented, or incorrectly documented.