was told on my last nic inspection that the smallest cable you can connect to a fused spur off a ring main is 1.5mm inspector picked me up on it as i had fed 150 w towel rail element through switched spur with 3 amp fuse fitted
 
out of interest which room in the house is the socket you have put the spur by?

Boiler - Kitchen

Thanks

- - - Updated - - -

Hello,

I changed the supply cable to 2.5mm twin and earth today. Thanks for your help.

Callum
 
was told on my last nic inspection that the smallest cable you can connect to a fused spur off a ring main is 1.5mm inspector picked me up on it as i had fed 150 w towel rail element through switched spur with 3 amp fuse fitted
That is correct if considering T&E from the ring to the FCU on power circuits.

Table 52.3
 
Boiler - Kitchen

Thanks

- - - Updated - - -

Hello,

I changed the supply cable to 2.5mm twin and earth today. Thanks for your help.

Callum

Emmmmmm! you have informed the Local Authority Building Control I hope as work is notifiable under Building Regulation Part P.
 
Boiler - Kitchen

Thanks

- - - Updated - - -

Hello,

I changed the supply cable to 2.5mm twin and earth today. Thanks for your help.

Callum

Oh dear that was my worry, now things have turned ugly, you do know that complecations now are apparent?
 