Hi
Hou need to run a supply to a piece of equipment which is rated at 63A SP, the run will mainly be underground in a duct and a 2c swa using the sheath as cpc.
My cable calculator is telling me I need to use a 50mm swa as the length of run is 100m but the equipment terminals won't take 50mm so what would you do?
i can't see there being room to mount a box to drop it down to 10mm so I'm stumped hence the question?