Hi
Hou need to run a supply to a piece of equipment which is rated at 63A SP, the run will mainly be underground in a duct and a 2c swa using the sheath as cpc.

My cable calculator is telling me I need to use a 50mm swa as the length of run is 100m but the equipment terminals won't take 50mm so what would you do?

i can't see there being room to mount a box to drop it down to 10mm so I'm stumped hence the question?
 
Hi
Hou need to run a supply to a piece of equipment which is rated at 63A SP, the run will mainly be underground in a duct and a 2c swa using the sheath as cpc.

My cable calculator is telling me I need to use a 50mm swa as the length of run is 100m but the equipment terminals won't take 50mm so what would you do?

i can't see there being room to mount a box to drop it down to 10mm so I'm stumped hence the question?


Have you tried doing a manual calculation to see if it comes out any different ?
 
What volt drop are you basing your calcs on? I think you might be able to use 25mm² if 5% is OK for your application.

Also, won't you be running your SWA into a local isolator (and then on to the load) anyway?
 
What volt drop are you basing your calcs on? I think you might be able to use 25mm² if 5% is OK for your application.

Also, won't you be running your SWA into a local isolator (and then on to the load) anyway?

I think the isolator is built into the equipment but even so it wouldn't take a 50mm.

thanks for the tip on 25mm I'll have another look at calculator, think it was at 5% but will check
 
Last edited:
Ok let me update here, correct me if I'm wrong but we have a max volt drop for buildings such as a cinema of 3%?

so I'm only allowed to drop 3% which is where the 50mm comes frfrom so I'm still stuck at termination how would you terminate a 50mm cable into a terminal which is designed for 25mm?
 
Ok let me update here, correct me if I'm wrong but we have a max volt drop for buildings such as a cinema of 3%?

so I'm only allowed to drop 3% which is where the 50mm comes frfrom so I'm still stuck at termination how would you terminate a 50mm cable into a terminal which is designed for 25mm?

You haven't yet said what the type of load is. If it involves lighting, then 3% max. If anything else, then 5%, unless otherwise specified by the manufacturer of the equipment.
 
You haven't yet said what the type of load is. If it involves lighting, then 3% max. If anything else, then 5%, unless otherwise specified by the manufacturer of the equipment.

Ok so its non lighting so I'm allowed 5% so 25mm is adequate, thanks much better than reducing pin crimps!
 
Last edited:
Couldnt you use crimps to get them in (cant remember the name though)

If not possible make off swa into mc adaptable box or similar then smaller cable from there.

Not dealt with cables that size but couldn't you use something like henley blocks to extend them as long as there in a sutable enclosure
 
Hi
Hou need to run a supply to a piece of equipment which is rated at 63A SP, the run will mainly be underground in a duct and a 2c swa using the sheath as cpc.

My cable calculator is telling me I need to use a 50mm swa as the length of run is 100m but the equipment terminals won't take 50mm so what would you do?

i can't see there being room to mount a box to drop it down to 10mm so I'm stumped hence the question?

I think everyone else has put enough information in to the thread for you. Now, i'll take this onto a slight tanjent and start a verbal slanging match between us fellow professionals as it's a much debated subject with no actual correct answer.

Anyhow - the part in question has been put into bold.

- Is the reason you are using 2core down to cost issues on the job? I avoid using the sheath like the plague, and i make sure its 3core using the BLACK - taped G/Y as the earth.

I feel personally, that using CPC's as the main earth is bad practice - corrosion can occur over time + some numpties don't tighten the glands properly.

So the question is....

1) Sheath as CPC
2) Seperate core as main CPC and strands as additional.

DEBATE! or fight, whichever :)
 
Mark this is just a personal thing here there is nothing wrong with using the sheath when it is adequate, correct glanding and installing will not see any issues like corrosion and loose glands... if this is the case then the competence of the electrician needs questioning not the method of earthing.... to be noted a loose gland still poses a risk even with separate earth core as it may be the fault route if the cable is damaged.
 
Mark this is just a personal thing here there is nothing wrong with using the sheath when it is adequate, correct glanding and installing will not see any issues like corrosion and loose glands... if this is the case then the competence of the electrician needs questioning not the method of earthing.... to be noted a loose gland still poses a risk even with separate earth core as it may be the fault route if the cable is damaged.

Yes i realise its personal mate, just thought id try and get something going to get some constructive input for a change.

I've seen glands heavily corroded that aren't fit for purpose - especially when they've been sat in a pool of water for 20years+. Strands can degrade - in most circumstances they don't/can't but in exceptional circumstances they can. And this is my reasoning behind always carrying an extra core.

I think we can question alot of electricians competence in todays world to be honest lol.

Your last point is a fair one though - but that comes down to again what you said, the competence of the electrician and the reliability of him installing the gland correctly. There is no doubt the sheath as the CPC is essntial and for this very reason, a split in one of the cores down the line would naturally go onto the strands. I always carry an extra CPC though - it was rammed into me as an apprentice so i'll never be shifted, set in my ways lol. + on a side note extra cores can come in handy further down the line. :)
 
In an ideal world the installation would be subject to regular inspections and testing in reality this isn't always the case and can fuel opinions of prefered methods but environment awareness and initial correct selection of equipment will see a good service and long life... its only when the environment changes that situations arise but again this is not in our control.... as long as we meet BS7671 at time of install then its up to the customer to periodic inspections are done and consultations are also done if the environment is changed .... we have enough weight on our shoulders already, worrying about the changes of circumstances out of our control isn't our problem ... we installed it correct at time to the conditions discussed at the time thus a good long service without corrosion ...job done - next job please ;)
 