There are some questions a proper electrician would be to embarrassed ask and the OP's is one of those questions

I suggest he should use a 120mm² swa should be more than enough to cover it
 
There are some questions a proper electrician would be to embarrassed ask and the OP's is one of those questions

I suggest he should use a 120mm² swa should be more than enough to cover it
wrong.

its 95.....

and VD comes out at 11.5
 
why is it these posters always joined say several years ago....have very few (if at all) posts....

then start asking about cable CSA...or RCD wont hold.....or garage: how to supply it...

Just a guess but........

Join forum when thinking about a career change to get some ideas. See the ads for the Electrical Trainee courses down the sidebar and start saving up. Complete course and start working for agencies/firms to get some experience. Cannot find stable employment due to being under qualified. Set up self employed and hit problems. Start posting on forum.

That would fit into the timescale.
 
Just a guess but........

Join forum when thinking about a career change to get some ideas. See the ads for the Electrical Trainee courses down the sidebar and start saving up. Complete course and start working for agencies/firms to get some experience. Cannot find stable employment due to being under qualified. Set up self employed and hit problems. Start posting on forum.

That would fit into the timescale.
Andy..
i would have it all stopped....all that lot...

shut down ...finished....
only one way...if you cant do the proper recognised route...you cant come in...

cant even understand why some in here would argue against that...

should be standard...
 
They bring our industry some class acts, part p was a inspired idea also!
 
Last edited by a moderator:
wrong.

its 95.....

and VD comes out at 11.5

I know 95mm² will do it I was waiting for the OP to correct me then again as I said 120mm² will more than do it and will have a bit to spare so it's not really wrong just at bit OTT
 
Last edited by a moderator:
and back to the OP , you say 230 mtrs?

pfft , forget it.

pulling that much swa of that size will require....

a. a team of men & a sh*t load of equipment

b. at least 3 through joints to piece individual section together cos you aint gonna get 230 mtrs of 120mm pulled in in 1 piece - trust me.

it it be easier to get a dno supply from an overhead pole if theres one knocking about.
 