Am on a job at the moment in a office it is a small extension with floor sockets going in on a new concrete floor, so hav to put a duct in before floor sockets go in. What do u recommend using flexible conduit, plastic conduit etc cheers
 
I have used high impact plastic conduit to the floor box vicinity ending with a coupler and a foot or so of steel flexible near the floor box to allow for adjusting it if necessary
 
Am on a job at the moment in a office it is a small extension with floor sockets going in on a new concrete floor, so hav to put a duct in before floor sockets go in. What do u recommend using flexible conduit, plastic conduit etc cheers
 
I guess you could use flexible but I'd pull the cables before the floor is thrown. I'd use standard conduit with the usual 2 bends maximum.
 
Only an amature or someone that knows no different would even think of installing that thin flexible conduit stuff. Good Quality heavy duty pvc conduit or even standard PVC conduit is the way to go for any containment wiring in concrete or screeded floors....
 
Only problem with steel is corrosion especially over time, I've come across many older steel conduits that you can't pull wires or cable through because the inside wall is very rough like sandpaper. Guess it's personal preference but I'd go with solid PVC conduit in slabs unless there was a good reason not to.
 

Reply to Cables in concrete in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, I have two questions regarding wiring and containment on commercial property stairwells in Ireland. We are currently wiring a 3 story...
Replies
10
Views
764
I'll start by saying - I have absolutely no intention of doing any wiring or anything electrical myself. You get someone professional to do a...
Replies
8
Views
915
Hello All. I'm quite new to this game and gaining experience, but going well in the main. My customer wants to feed a Hob ( on island in centre...
Replies
5
Views
247
Some advise or views would be appreciated. My supply is 100 amp single phase. I purchased my property 3 years ago or so, the owner prior to the...
Replies
29
Views
968
I have been asked to change cu from old fuse board which has 6 fuses. Only 4 fuses are used. The first fuse feeds cooker circuit. This is not used...
Replies
17
Views
864

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock