I wish they'd change the diagram to show two correctly spaced holes, and not an oval then! I don't see the problem with a slot, really, as the centre part of the joist takes very little load, which allows 'engineered' joists like this to work.

I-JOIST.jpeg
 
I would not do anything for free, but should compliance with current regs not be a consideration if changing the circuit characteristics IYO

Not necessarily. I will give you good example. Three or four years ago, i wired a conservatory up. It was built off the existing dining room, and i took a spur through the wall from an existing socket, which was part of the downstairs ring final, protected by a 3036 fuse. I installed a SFCU RCD type, and ran my cables as required, i did however ensure that the existing was up to the job of being added to, as this is our responsibility as you know.

My part of the install is 17th compliant, the existing install isn't. It was done like this because it was the easiest and cheapest fix. It would have been my preference to bring the ring final into the new age, but this would have involved a lot of grief and expense for the customer, and she had no real desire for me to destroy her kitchen or to pay me the £600 plus quid i quoted to replace CU etc.

Sometimes it is easier and cheaper to upgrade, and this is the preferred option wherever possible, but it is not a must do.

I hope i didnt come across as a bit sharp with my last post, but i find it frustrating that some people think that they are duty bound to correct every little non compliance, and quite a lot of large non compliances all for the princely sum of NO CHARGE. This is not and never will be the case. We have a duty of care to highlight any issues, and our consciences should promote this, but as the saying goes "we can only take the horse to the water, we cant make it drink"

Cheers.............Howard
 
I submitted the thread for constructive opinions both negative and positive, it is just a bone of contention on many insurance jobs that I attend.

Thank you all for your responses.
 
Talking of the guidance diagram in the OSG, is it acceptable to make oval holes in joists, as it shows, formed by joining up two adjacent holes? I ask as the diagram shows an oval, but the text only mentions holes, and that they need to be three diameters apart.

I think you've misunderstood the diagram. The shaded brown areas show the permited locations for notches and holes.

It's not an illustration of a notched or holed joist. If it was, you'd see the material thickness through the hole.
 
Ah I see what you mean. Trouble is, in the OSG version, it does show the shadow of the material thickness. I would have thought that a slot would be less weakening to the beam than the equivalent separate holes. Still, I,m no structural engineer, what do I know...?

holes.jpg
 
I wish they'd change the diagram to show two correctly spaced holes, and not an oval then! I don't see the problem with a slot, really, as the centre part of the joist takes very little load, which allows 'engineered' joists like this to work.

I-JOIST.jpeg

Your wish has come true! They changed the diagram as you suggested in the new green on-site guide (page 73)

I found the old diagram confusing. I think that it was supposed to illustrate a zone where holes could be drilled though, rather than a slot.
 
Talking of the guidance diagram in the OSG, is it acceptable to make oval holes in joists, as it shows, formed by joining up two adjacent holes? I ask as the diagram shows an oval, but the text only mentions holes, and that they need to be three diameters apart.

How many electricians actually adhere to these rules, ie holes 2 diameters apart, only within the 0.25-0.4 x span zone, etc? Most I have seen in my limited experience don't.

Notches.gif

Where was your original diagram taken from, Stroppy? The position and depth of notching is different to the diagram in both my On Site Guides and my old copy of the Electrician's Guide to the Building Regs (which you've also posted).
 
How many electricians actually adhere to these rules, ie holes 2 diameters apart, only within the 0.25-0.4 x span zone, etc? Most I have seen in my limited experience don't.

Never mind the sparkies .... what about the plumbers who run motorways of copper pipe in notches like cheddar gorge anywhere on the joist that they can get a board up?
 
Where was your original diagram taken from, Stroppy? The position and depth of notching is different to the diagram in both my On Site Guides and my old copy of the Electrician's Guide to the Building Regs (which you've also posted).
The B&W one was from searching Google for "joist drilling zones" or similar, as I couldn't find an image of the OSG one, and couldn't be bothered to get mine from the van and scan it, like I did for the colour one. I didn't take any notice of the notches figures as I've never had to notch so far.
 
Drilling joists is another bone of contention with me as well. There are drawings, diagrams, and bollox galore on this subject. In the ideal world we would be able to comply, in the real world, it is almost always impossible. Again, the "regs" will take second place to good old common sense!

If you use your brain, all you need to achieve;

1, Dont weaken the joist any more than you need to, this is why we try to get them central, and space them out.
2, Make sure the drilled holes are in the best place possible to keep the cables out of harms way.

Its obvious to a blind man, that if you need to go through a bit of 2x4, you need to be a bit more accurate then if you a 10x5 joist.

Cheers..............Howard
 
I agree it is often impossible or impractical to do it 'right', and a couple of 25mm holes in the naughty-zone of a 120mm joist is hardly likely to make the floor collapse.

I just found this which illustrates why the zones are where they are:

Critical+zones.jpg
 