I have been looking at this today and found it interesting so thought i would post a question for any of you to answer.
Calculate the neutral current on a lv 3 phase system.
L1 = 30Amps
L2 = 60Amps
L3 = 22Amps.
SQRT I²A + I²B + I²C - (IA x IB) - (IB x IC) - (IC x IA)
and if the answer is not 42, then i'm out. there's beer to be drunk. but a head guess is 24amps odd.
It's when you lose the neutral it starts getting interesting! :-)
34.69870315. so i'll give you 34.7. LOL.
a rough guess ( and i mean rough) to check if you've don the calc. correctly ( i.e. not got way out) is to add the 3 line currents and divide by 3.
Or a little cheat I like is to use a line measurement representing L1 in cm, then draw a line representing L2 from the end point of line 1 at 120 degrees from line 1, then a third line representing L3 from the end point of line 2 at 120 again. The distance between the end point of line 3 and the start point of line 1 will represent the neutral current. It will look something like this:
p.s. Don't let your college lecturers see you doing this! lol
if you did it in inches, would the neutral current be 2.54 x as large? :rofl:
Could you explain this a bit more please. Do you mean where a neutral is not required?
As the previous poster hinted, things go haywire!!!
On an unbalanced star, if you lose the neutral, depending on the 3 loads, the star point wanders away from zero for starters!
I've got a link to an excellent book which will explain all.
You'll have to remind later though, too tired at the moment.
Cool thanks for the link, ill be sure to buy a copy, watersones have it and a family member can get me a 50% discount;)
HANDY!!!
I might be getting in touch with you sometime soon. :-)
Better warn you, it is quite heavy/theoretical, but has loads of worked examples, which is always good.
South West, Bath
Calculating Neutral current in unbalanced TP
Electrical Course Trainees Only
Simonslimline,
Silly Sausage,
