Calibration Checkbox | on ElectriciansForums
Discuss Calibration Checkbox in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
diditrain
north west
Recently had my multi-function tester calibrated and have been getting my baseline readings against a checkbox.
I have checked continuity on every resistor and all are within specification.
I have also done insulation resistance on every resistor and every one is within tolerance levels, except the 50 meg ohms one. I tested at 500v and the reading was 44.4 meg ohms.
Should i be concerned?
how do you know that the 50Meg. resistor is 50Meg.? also at that sort of value, a bit of moisture in the air can give you a lower reading.
I thin I remember that the checks are recommended monthly by Elecsa, you may have other instructions with the calibration check box, but monthly seems reasonable. Just remember to keep records of your testing so you can identify trends.
Reply to Calibration Checkbox in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
I'd speak to an independant company about fixing this, you'd expect it to be a relatively simple adjustment and not require much in the way of...
davesparks
Ok so just done a quick test on mine. Megger mft on high gives 0.30 Robin 4120dl on 20ohm hives 0.22 Robin 4120 on 200ohm gives 0.28 Bearing in...
Recommended Sponsor News
Hi everyone,