Discuss Calibration Checkbox in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
diditrain
Recently had my multi-function tester calibrated and have been getting my baseline readings against a checkbox.
I have checked continuity on every resistor and all are within specification.
I have also done insulation resistance on every resistor and every one is within tolerance levels, except the 50 meg ohms one. I tested at 500v and the reading was 44.4 meg ohms.
Should i be concerned?
how do you know that the 50Meg. resistor is 50Meg.? also at that sort of value, a bit of moisture in the air can give you a lower reading.
I thin I remember that the checks are recommended monthly by Elecsa, you may have other instructions with the calibration check box, but monthly seems reasonable. Just remember to keep records of your testing so you can identify trends.
Reply to Calibration Checkbox in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Hi all My Fluke tester failed on one test today while having it's annual calibration, the continuity resistance test current. Test Current -...
Hi guys, Had an issue at a recent survey where doing a quick check and found we had pme with a reading of 0.44 ohms. Called the network and they...
I've managed to mainly fix a Megger 1502 MFT that was so far out of calibration it got laughed out of a tester day. I have high current loop. rcd...
Bit of a long shot on here but does anyone have a circuit diagram for a Chavin Arnoux CA 6545 5kV tester? I've copied my post on EEVBLOG forum...