Just inspected a shower, found someone used 10mm yellow/green cable as live and neutrol conductor, the csa is no problm, but does yellow/green cable has the same insulation sheath with grey cable? i assume this is fine, but hope to get some confirmation...

cheers
 
Last edited:
A CPC (circuit protective conductor), should NEVER be used as a live conductor.

What sort of cable is being used then? You mention 10mm cable and grey cable ???
Is the cable being used not a 10mm pvc with brown , blue and earth?? Or is it swa ?

Thanks and regards,
Sav
 
A CPC (circuit protective conductor), should NEVER be used as a live conductor.

What sort of cable is being used then? You mention 10mm cable and grey cable ???
Is the cable being used not a 10mm pvc with brown , blue and earth?? Or is it swa ?

Thanks and regards,
Sav

Sounds to me like they are 10mm² singles (6491x) as they are both green/yellow.

The insulation is the same as any other colour singles.
 
Last edited by a moderator:
yes, they are in conduit, i assume the installer was short of grey color cable so just put 2 no 10mm yellow/green cable and 1 no 4 mm earth cable inside
 
Ahhh, I see. Still though, the earth (green/yellow) should not be used as a live conductor.

So does that mean the shower does not have an earth supply? Is it a plastic shower, as in no metal exposed parts ?
 
So whoever installed the wiring used 2 x 10mm green / yellow 1 x 4mm green /yellow ???

Is that all they had in their van !!! Was screwfix or any other wholesaler not open that day !!!

How did they terminate at the board then or the isolator?? Did they bell each cable out !! Very suspect to me and definate code 2 to say the least .
What do you guys think?? Am i going over the top and all is ok?
Best regards,
Sav
 
It is prohibited by the Regulations.

A green/yellow single core cable may not be oversleeved and used as a live conductor.

You could argue that it presents an immediate danger.
 
514.4.2 "Single core cables that are coloured green-and-yellow throughout their length shall only be used as a protective conductor and shall not be over-marked at their terminations, except as permitted by Regulation 514.4.3 [use as a PEN conductor]."
 
:eek: as its in conduit, shouldnt be too hard to pull out and do properly.As said on previous post , doubtful it was ever tested and if it was a new circuit how were certs issued?? if at all. " rip it up & start again"!
 
Earth cable g/y sleeving should never be used for LINE conductor NEVER

Can't be used as a live conductor. The use of a green/yellow single core cable for a neutral conductor is equally prohibited as its use as a line conductor.
 
So whoever installed the wiring used 2 x 10mm green / yellow 1 x 4mm green /yellow ???

Is that all they had in their van !!! Was screwfix or any other wholesaler not open that day !!!

How did they terminate at the board then or the isolator?? Did they bell each cable out !! Very suspect to me and definate code 2 to say the least .
What do you guys think?? Am i going over the top and all is ok?
Best regards,
Sav

I agree with you all the way you are not over the top
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined

Thread Information

Title
can 10mm yellow/green cable used for live conductor?
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
14

Advert

Thread statistics

Created
bluesky,
Last reply from
scon66,
Replies
14
Views
5,917

Advert

Back
Top