I wanted to slightly re-route a badly routed 6mm2 twin and earth flat cable, that leaves my utility room through the plasterboard, the wall and then to a junction box on the outside wall. I disconnected the Wago connectors in the junction box and pulled the cable through, but now can't get the dam thing to fish back through. I tested with a scrap piece of cable and it does (with some fiddling) fish back from the outside.

I'm happy to be told I need a professional, but if possible I'd like to try and rectify this myself.

First option I thought would be to use a fishing tool, but the ones I see online seem to be for smaller cables and there is very little room in the hole though the wall.

Second option is to cut the cable fish back through some outside and then reconnect in a junction box which would be visible for inspection.

Third option would be to cut the cable and then reconnect using crimps and seal with heat shrink.

Please be kind, I already feel like a plonker!

Thanks.
 
but now can't get the dam thing to fish back through. I tested with a scrap piece of cable and it does (with some fiddling) fish back from the outside.
Can you still fish through another cable?

If not then probably hole blocked by something inside moving. (As above, try long masonry drill)

If yes then use that to pull the 6mm back through? Need a good mechanical joint, often just run/wrap side-by-side for 30cm or so and tape together, tape can also make the end more "pointed" so less to catch on edges of holes, etc.
 
If the T&E is outside, use another bit of cable / flex / coat hanger pushed through from the inside and join the T&E onto it by making a loop on each end and wrap all the joint in tape to stop anything catching on the way back through the hole.
 
Thanks all

I only have a hand drill (rather than an SDS drill) but do have a 12mm masonry bit so I’ll try to make the hole clearer.

T&E is on the inside and I’m trying to fish it outside. I can just fish a cable the same type from the outside in so I can attempt to join the 2 together and then pull back through.

Silly question time, how do I put a loop on the end of a cable to join them?
 
In addition, can someone please point me in the direction of where to get suitable heat shrink should I go down this route? My web searches have made me even more confused.
 
Crimps and heat shrink alone do not a complete joint make. Beware many crimps are not rated highly enough for a 6mm² circuit, nor are most suitable for the solid CPC. Good crimps that are adequate for the job require installation using a calibrated tool to achieve correct rating, and the whole should then be enclosed in a box with the cables anchored to provide strain-relief. I know a lot of sparks crimp-and-conceal without these niceties but it's not correct practice.

BTW Does the T+E itself run outside?
 
Either twist the copper together or tape it onto the cable and pull it through. Sometimes it can be fiddly fishing through a wall, clear out the hole and use a coat hanger and it shod go back through.
 
Crimps and heat shrink alone do not a complete joint make. Beware many crimps are not rated highly enough for a 6mm² circuit, nor are most suitable for the solid CPC. Good crimps that are adequate for the job require installation using a calibrated tool to achieve correct rating, and the whole should then be enclosed in a box with the cables anchored to provide strain-relief. I know a lot of sparks crimp-and-conceal without these niceties but it's not correct practice.

BTW Does the T+E itself run outside?
Ok thanks - one to leave to the pros then. No it’s connected via a junction box to an SWA cable that runs to my shed.
 
Can you borrow a large drill?
a 20 or 25mm hole is much easier to fish through.
 
When they say “join” the cable to pull it through, it’s not an electrical joint.

What I do, is strip back maybe 6 or 8 inches off the outer sheath and the inner insulation.
Cut off the L and N so you’re left with the bare copper earth.
Loop it over, and twist it around itself.
Do the same with the other side, but it can be a smaller cable… it’s just for pulling through.

Squeeze the loops up with pliers to make it smaller than the size of the cable that you know the hole is big enough to take.

If it sticks, wrap tape round the joint to make it smooth… still tight, rub it up with some fairy liquid as a lubricant.

Messy job, but it can work.


I agree though that something has dropped in the hole, and it’s at such an angle that it only allows one way travel. Best to clear that somehow.

Use your 12mm bit and try and tap it through with a hammer. You’re just trying to shift a blockage, not drill a new hole.
 
When they say “join” the cable to pull it through, it’s not an electrical joint.

What I do, is strip back maybe 6 or 8 inches off the outer sheath and the inner insulation.
Cut off the L and N so you’re left with the bare copper earth.
Loop it over, and twist it around itself.
Do the same with the other side, but it can be a smaller cable… it’s just for pulling through.

Squeeze the loops up with pliers to make it smaller than the size of the cable that you know the hole is big enough to take.

If it sticks, wrap tape round the joint to make it smooth… still tight, rub it up with some fairy liquid as a lubricant.

Messy job, but it can work.


I agree though that something has dropped in the hole, and it’s at such an angle that it only allows one way travel. Best to clear that somehow.

Use your 12mm bit and try and tap it through with a hammer. You’re just trying to shift a blockage, not drill a new hole.
Great advice thank you - will give this a shot.
 