Hi,

I wanted to slightly re-route a badly routed 6mm2 twin and earth flat cable, that leaves my utility room through the plasterboard, the wall and then to a junction box on the outside wall. I disconnected the Wago connectors in the junction box and pulled the cable through, but now can't get the dam thing to fish back through. I tested with a scrap piece of cable and it does (with some fiddling) fish back from the outside.

I'm happy to be told I need a professional, but if possible I'd like to try and rectify this myself.

First option I thought would be to use a fishing tool, but the ones I see online seem to be for smaller cables and there is very little room in the hole though the wall.

Second option is to cut the cable fish back through some outside and then reconnect in a junction box which would be visible for inspection.

Third option would be to cut the cable and then reconnect using crimps and seal with heat shrink.

Please be kind, I already feel like a plonker!

Thanks.
 
but now can't get the dam thing to fish back through. I tested with a scrap piece of cable and it does (with some fiddling) fish back from the outside.
Can you still fish through another cable?

If not then probably hole blocked by something inside moving. (As above, try long masonry drill)

If yes then use that to pull the 6mm back through? Need a good mechanical joint, often just run/wrap side-by-side for 30cm or so and tape together, tape can also make the end more "pointed" so less to catch on edges of holes, etc.
 
If the T&E is outside, use another bit of cable / flex / coat hanger pushed through from the inside and join the T&E onto it by making a loop on each end and wrap all the joint in tape to stop anything catching on the way back through the hole.
 
Thanks all

I only have a hand drill (rather than an SDS drill) but do have a 12mm masonry bit so I’ll try to make the hole clearer.

T&E is on the inside and I’m trying to fish it outside. I can just fish a cable the same type from the outside in so I can attempt to join the 2 together and then pull back through.

Silly question time, how do I put a loop on the end of a cable to join them?
 
In addition, can someone please point me in the direction of where to get suitable heat shrink should I go down this route? My web searches have made me even more confused.
 
Crimps and heat shrink alone do not a complete joint make. Beware many crimps are not rated highly enough for a 6mm² circuit, nor are most suitable for the solid CPC. Good crimps that are adequate for the job require installation using a calibrated tool to achieve correct rating, and the whole should then be enclosed in a box with the cables anchored to provide strain-relief. I know a lot of sparks crimp-and-conceal without these niceties but it's not correct practice.

BTW Does the T+E itself run outside?
 
Either twist the copper together or tape it onto the cable and pull it through. Sometimes it can be fiddly fishing through a wall, clear out the hole and use a coat hanger and it shod go back through.
 
Crimps and heat shrink alone do not a complete joint make. Beware many crimps are not rated highly enough for a 6mm² circuit, nor are most suitable for the solid CPC. Good crimps that are adequate for the job require installation using a calibrated tool to achieve correct rating, and the whole should then be enclosed in a box with the cables anchored to provide strain-relief. I know a lot of sparks crimp-and-conceal without these niceties but it's not correct practice.

BTW Does the T+E itself run outside?
Ok thanks - one to leave to the pros then. No it’s connected via a junction box to an SWA cable that runs to my shed.
 
When they say “join” the cable to pull it through, it’s not an electrical joint.

What I do, is strip back maybe 6 or 8 inches off the outer sheath and the inner insulation.
Cut off the L and N so you’re left with the bare copper earth.
Loop it over, and twist it around itself.
Do the same with the other side, but it can be a smaller cable… it’s just for pulling through.

Squeeze the loops up with pliers to make it smaller than the size of the cable that you know the hole is big enough to take.

If it sticks, wrap tape round the joint to make it smooth… still tight, rub it up with some fairy liquid as a lubricant.

Messy job, but it can work.


I agree though that something has dropped in the hole, and it’s at such an angle that it only allows one way travel. Best to clear that somehow.

Use your 12mm bit and try and tap it through with a hammer. You’re just trying to shift a blockage, not drill a new hole.
 
When they say “join” the cable to pull it through, it’s not an electrical joint.

What I do, is strip back maybe 6 or 8 inches off the outer sheath and the inner insulation.
Cut off the L and N so you’re left with the bare copper earth.
Loop it over, and twist it around itself.
Do the same with the other side, but it can be a smaller cable… it’s just for pulling through.

Squeeze the loops up with pliers to make it smaller than the size of the cable that you know the hole is big enough to take.

If it sticks, wrap tape round the joint to make it smooth… still tight, rub it up with some fairy liquid as a lubricant.

Messy job, but it can work.


I agree though that something has dropped in the hole, and it’s at such an angle that it only allows one way travel. Best to clear that somehow.

Use your 12mm bit and try and tap it through with a hammer. You’re just trying to shift a blockage, not drill a new hole.
Great advice thank you - will give this a shot.
 
Ok thanks - one to leave to the pros then. No it’s connected via a junction box to an SWA cable that runs to my shed.
First thing is you should avoid cutting and joining if at all possible!

If you are joining inside and in some accessible location (i.e. not buried in a wall, etc) then you have more choices for junction boxes. For example, this will easily deal with 6mm or 10mm T&E cable:

However, if it is going to be hidden then it needs to be a maintenance-free version. Those are typically designed around spring-loaded terminals like the Wagos, along with cable restraint, etc, so they will not loosen due to normal levels of vibration and temperature cycling. But you have to be careful as not all combinations of, for example, Wago boxes and terminals are rated for that, and 6mm is larger than some of the Wago family's max size rating. Also you really need to check the instructions as some specify the box has to have additional cable ties (not supplied!) to hold it shut if it is to meet the MF rating.
 
First thing is you should avoid cutting and joining if at all possible!

If you are joining inside and in some accessible location (i.e. not buried in a wall, etc) then you have more choices for junction boxes. For example, this will easily deal with 6mm or 10mm T&E cable:

However, if it is going to be hidden then it needs to be a maintenance-free version. Those are typically designed around spring-loaded terminals like the Wagos, along with cable restraint, etc, so they will not loosen due to normal levels of vibration and temperature cycling. But you have to be careful as not all combinations of, for example, Wago boxes and terminals are rated for that, and 6mm is larger than some of the Wago family's max size rating. Also you really need to check the instructions as some specify the box has to have additional cable ties (not supplied!) to hold it shut if it is to meet the MF rating.
Thanks for the advice.

Yes I’ll be cutting as a last resort, I should get it fed through eventually.

That junction box looks better than the ones I looked at. Are there any regs specific to these type of junction boxes I need to be aware of? More for my curiosity.
 
Got it fished in the end - I did as suggested and fed another cable through from the outside and taped it to the cable I wanted pulled back through, and with a bit of fairy liquid it came out. It worked without me needing to twist any wires together, I don’t have much wiggle room to remove cable so luckily this worked.

Will give you a laugh though - I got it fished first and gave myself a high-five when I realised I hadn’t re-routed the dam thing! Could have slapped myself…

Great forum this, thanks for all your suggestions.
 
Got it fished in the end - I did as suggested and fed another cable through from the outside and taped it to the cable I wanted pulled back through, and with a bit of fairy liquid it came out. It worked without me needing to twist any wires together, I don’t have much wiggle room to remove cable so luckily this worked.

Will give you a laugh though - I got it fished first and gave myself a high-five when I realised I hadn’t re-routed the dam thing! Could have slapped myself…

Great forum this, thanks for all your suggestions.
We've all been there. Fitted quite a few commando plugs without putting the base on before
 

Reply to Can't fish cable back through in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I live in a warehouse condo, converted about 20 years ago. The building dates to about 1870 but with the conversion, all of the electrical was...
Replies
3
Views
480
My wife has a electric heated airer, our dog chewed through the cable and I thought it would be no different from rewiring a plug. It's not. I...
Replies
2
Views
762
I am installing some driveway lights. The customer wants to be able to switch them on from t he house, but also have a PIR at the driveway...
Replies
12
Views
632
DIYer here. I'd like to install an electric car wall charger myself. It calls for 6/2 romex which I have. Unfortunately my panel is in my...
Replies
0
Views
645
We have a room in the house that was the kitchen. That has been relocated to a different area, so the old kitchen has been sold off and the room...
Replies
2
Views
618

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock