A
Adrian Sadler
The alternator manual has the wiring diagram inside. Its a portable genny with a floating earth it seems
The alternator manual has the wiring diagram inside. Its a portable genny with a floating earth it seems
Well i couldnt find it in the Wiring Regs .. but TLC
"All metal parts of the caravan, with the exception of metal sheets forming part of the structure, must be bonded together and to a circuit protective conductor, which must not be smaller than 4 mm² except where it forms part of a sheathed cable or is enclosed in conduit."
https://www.tlc-direct.co.uk/Book/7.9.2.htm
I think what you are after is how to test a Caravans Wiring, so basically a Full Periodic Inspection that should be done every 3yr and the RCD tested every time you use it.
Rather than gonto the pub im gonna swat up on the regs and see whats what. If i dont understand ill give it a swerve. I do understand whats your saying about declining but it would be nice to understand whats going on and educate myself.
Ive spent years as an electrician but yer always learning....
there is usually an earth terminal on the genny, just take a cable from there to the supply.Right. After a bit of digging the genny has a floating earth.
In the manual it says it must be earthed (guessing via a rod)
all the cpc's that go back to the board and then staked.
From what ibhave read on other forums and genny sites - the 'best' way for a genny feeding a van is to link Earth to neutral in the genny or make a specific lead and stake it.
Any of this make sense to anyone? Would this then create a tn system? Head explode brewing.
In the regs book there are pictures showing the setup thats currently in place where its fed from a genny and all earth point for sockets/lights etc all bonded together
Right. After a bit of digging the genny has a floating earth.
In the manual it says it must be earthed (guessing via a rod)
all the cpc's that go back to the board and then staked.
From what ibhave read on other forums and genny sites - the 'best' way for a genny feeding a van is to link Earth to neutral in the genny or make a specific lead and stake it.
Any of this make sense to anyone? Would this then create a tn system? Head explode brewing.
In the regs book there are pictures showing the setup thats currently in place where its fed from a genny and all earth point for sockets/lights etc all bonded together
there is usually an earth terminal on the genny, just take a cable from there to the supply.
correct me if im wrong but what is the point in a rod?
so you have a rod at the genny and another at the caravan right next to it?
supply of caravan i mean, yes earth the genny but i would take the earth direct to the genny rather than another rodWhat supply?
The point of a rod (combined with a N-E link) with a generator is normally to make one of the lines be a neutral and reference this to the mass of earth. The same way that earthing the star point of a transformer does.
No they have one rod which they install when running from the generator and hopefully don't install when they are running from a mains supply.