Recommendations I've suggested are,
1. Fit 63amp mcb in 100mA rcd enclosure to protect 16mm cable. (currently protected by dno 100amp fuse)
Make that an S type 100 or 300mA RCD......
2. Disconnect existing earth rod at supply end and pme supply cable to outside dist. board.
I wouldn't bother disconnecting the earth rod connection, leave it in....
3. Replace 30mA rcd at dist board and fit main switch, replace 10 amp with 32amp mcb's that supply hookup sockets (currently there is a 6mm 3core that supplies 2 x sockets, 2 live cores sharing a neutral)
Not sure what you mean by (2 live cores sharing a neutral)??
4. Fit new hookup enclosures containing 2 x10 amp 30 mA rcbo and 2 x 16 amp socket outlets ( caravan club apparently recommend 10a mcb?)
Fine, so long as the RCBO's are DP not SP!!
5. Isolate pme supply at hookup and install earth rod at each one.
Fine, remember the hook up cabinet can be PME, it is the supply to the caravan that needs to be isolated and on a TT earth... The hook-up cabinets i've seen for caravan pitches have two small earth bars, one for the incoming earth (pme) and one for the TT earth.
What's your thoughts? I know it's not ideal but short of ripping it all out and starting again, which isn't gonna happen!!