Hi all,
Currently changing out a ceiling rose on my property which was built in the 50/60’s with old wiring.
Coming from the ceiling is 1x cable (live, neutral and earth), wired through choc blocks straight to the pendant light.
In the light switch is 1x cable (live, neutral & earth). However the earth is not terminated. Live is in the common and neutral in L1.
On the ceiling rose, can I put the incoming live and outgoing light live together and put the neutrals together?
Thank you
 
This sounds like really old wiring using junction boxes, that was the usual way of doing things before loop in roses became the norm.
If that's the case, you can extend onwards from your existing light to another light, if that's what you're trying to do, BUT the earth wire needs to be verified that it connects back to the earth terminal in your fuse box. Earth wires in lighting circuits for class 2 lighting fittings weren't compulsory until the end of the '60s, and it wasn't unusual to find some earth wires 'floating'.
 
This sounds like really old wiring using junction boxes, that was the usual way of doing things before loop in roses became the norm.
If that's the case, you can extend onwards from your existing light to another light, if that's what you're trying to do, BUT the earth wire needs to be verified that it connects back to the earth terminal in your fuse box. Earth wires in lighting circuits for class 2 lighting fittings weren't compulsory until the end of the '60s, and it wasn't unusual to find some earth wires 'floating'.
Thank you for replying, I did think it was a very old way of doing things! I am not trying to extend to another light, I am just trying to change it to a modern ceiling rose but what was there before was just choc blocks
 