Hello everybody! I just wanted to ask, what would be the best practise to run circuits for white goods?
In my plan what i see is:
1. Fridge & Freezer 20 amp RCBO radial wired with 2.5mm
2.Washing machine 20 amp MCB Radial 2.5mm
3. dish washer 20 amp mcb radial with 2.5mm
4. Washing machine and dish washer 32 amp mcb wired 2.5mm ring final.

Please advice what is the best practise to do it? would it be too much having dish washer and washing machine on separate circuits or just wire them both on ring final?

Also advice me please with mcb sizes if i am correct about radials. As far as i rememmber from regs maximum mcb rating for radial is 16amp.

Thank you
 
If this is a domestic set up, a single 2.5mm2 radial fed by a 20A RCBO is adequate for all three, if the water heating elements in the dishwasher and washing machine are 2kW.
If either are 3kW, then a 4mm2 radial fed by a 32A RCBO will do, but the washmac. and dishwasher shouldn't both be plugged into the same double 13A s/socket.
 