How would others code the switch fuse not meeting IP4X on the top surface?
The live terminals are very close to the top edge
Screenshot_20240110_101613_Gallery.jpg
Screenshot_20240110_101604_Gallery.jpg
 
Hmm. Should be fitted with a tails shroud (or a dob of silicone).

Doesnt meet IP4x but you ain't going to get your finger in there. In the real World - C3.
 
It's in a communal cupboard what if someone put there car keys there while checking the meter? Is silicon conductive before it dries.
ip4x is a 1mm piece of wire,ip2x refers to a bs finger
 
These kind of nibble outs have always naff and normally nearly always leave a gap around the cable entry. Most sparks will squidge a bunch of mastic around the gaps but it still looks rubbish
 
It's in a communal cupboard what if someone put there car keys there while checking the meter? Is silicon conductive before it dries.
ip4x is a 1mm piece of wire,ip2x refers to a bs finger
Or decided to take their metal knitting needles in there. I was trying to make a sensible risk assessment.
Silicone is not conductive snd - in any case - why touch it while it’s wet?

But we are now talking about resolution of the issue. I thought you were doing an EICR?
 
I would C3 this too
 
  • Agree
Reactions: mainline
I think as electricians we over egg this IP4X jazz. If I can't see live parts without the use of laboratory equipment then Code 3 if I'm in a bad mood.
 
You can see the terminals from the top, in any case work has asked me to address the issue,so I spilt some 16mm blind grommets with a bit of ct1 to keep in place
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread starter

newfutile

Arms
Supporter
~
Joined
Location
hemel hempstead
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Electrical Engineer (Qualified)

Thread Information

Title
Click UK switch fuse
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
7

Advert

Thread statistics

Created
newfutile,
Last reply from
newfutile,
Replies
7
Views
1,254

Advert