It is only required for cables that are buried in the walls and may be nailed into or such, not for cables passing through a wall as they cannot readily be damaged.
 
It is only required for cables that are buried in the walls and may be nailed into or such, not for cables passing through a wall as they cannot readily be damaged.

Or for those socket outlets intended to supply outdoor equipment, regardless of installation method.

Richard, I was hoping driverman would read through the regs and give us his opinions. :)
 
I've seen high Zs's for RFC on fairly new installs but only because a type C RCBO was used ,if a type B had be used then the Zs would be satisfactory .So would there be any reason to change the RCBO to a type B so that the circuit is within the maximum earth loop? . I've never sited this as a deviation on a EICR as the disconnection time is achieved by the RCBO although I feel its an over site in the design stages.

Could be a type C for a reason? Also if you do change it to a type B as with all breakers make sure its in the permissable maximum values if the circuit is tested cold and dont just go off the table in the regs.

And yes i would change it to a type B from a C to bring it into the permitted Zs.

im not sure if iv understood the post correctly with this reply to be honest haha so apologies if this seems a little arsey.
 
The circuits in question were for feeding 6 socket on a RF in school classroom for general use only 1 computer and a white board so could not see a reason for the C type . It was an EICR that identified this so maybe I should of sited it as a code 3. I have noticed that in general Merlin Gerin RCBOs are type C
 