It is only required for cables that are buried in the walls and may be nailed into or such, not for cables passing through a wall as they cannot readily be damaged.

I've seen high Zs's for RFC on fairly new installs but only because a type C RCBO was used ,if a type B had be used then the Zs would be satisfactory .So would there be any reason to change the RCBO to a type B so that the circuit is within the maximum earth loop? . I've never sited this as a deviation on a EICR as the disconnection time is achieved by the RCBO although I feel its an over site in the design stages.