Disagree supplementary bonding connects to all exposed conductive parts...Rcd protection required.
You seem to think all the issues you have raised come under one code. It doesn't and each issue is treated separately.
1.IPX4 230v lights in zone 1...... Compliant so no code regardless of additional protection.
2.Lack of additional protection by means of 30ma RCD to bathroom lighting circuit......either a code 2 or 3 dependant on the presence of SB.
3. Lack of SB......either code 2 or 3 dependant on the presence of additional protection by means of 30ma RCD to all final circuits within the bathroom.
 
You seem to think all the issues you have raised come under one code. It doesn't and each issue is treated separately.
1.IPX4 230v lights in zone 1...... Compliant so no code regardless of additional protection.
2.Lack of additional protection by means of 30ma RCD to bathroom lighting circuit......either a code 2 or 3 dependant on the presence of SB.
3. Lack of SB......either code 2 or 3 dependant on the presence of additional protection by means of 30ma RCD to all final circuits within the bathroom.
Agree...2 & 3 are the important ones there C2
 
To be honest you don't find that many bathrooms with steam rooms in them and even then the "steam" isn't at full temperature as above 59°C your skin will start to blister.
I assume by steam you mean the water vapour that subsequently forms condensation damaging the fittings in which case I have seen some quite badly corroded fittings over the years
I don't work in the sort of market that has steam rooms (unfortunately).

I've seen a few corroded fittings in my time certainly, but never actually one that has failed in an unsafe way - maybe just luck. Replaced plenty of pendant fittings in bathrooms of a certain age too and most of those have been surprisingly good condition still, even if within zone 1 (or very close to).
 
I don't work in the sort of market that has steam rooms (unfortunately).

I've seen a few corroded fittings in my time certainly, but never actually one that has failed in an unsafe way - maybe just luck. Replaced plenty of pendant fittings in bathrooms of a certain age too and most of those have been surprisingly good condition still, even if within zone 1 (or very close to).
For corrosion at it's worst it has to be the swimming pool plant room and the fittings around the pool itself, the chlorine and the chlorine vapour destroys everything it comes into contact with it is very rare to repair equipment it is almost always a replace
 