I'm going to replace a non-maintained emergency light above a communal front door of residential flats. It's the first such luminaire I've installed in a while. The manufacturer instructions specify to initially charge for 24hrs, then test for duration of 3 hours. Issue is, I suspect (haven't got access to the service cupboard yet), is that the key switch isolates the other existing EL's. I've read somewhere, not to carry out a full test, if the property is going to be occupied after the test. Can anyone advise or point me to the relevant regulations for commisioning EL's.
 
Residential flats they will always be occupied after the test, you have no option but to test.

I would have powered it up for 24hrs before I fitted it, then wired it up and test immmediately.
 
Connect up and charge as required for 24hrs then do a "disconnect" at the actual light itself to test for 3 hrs (i.e. only that emerg lite will come on and not the rest)

Provided you arent discharging all the emerg lites at one sitting then there isnt a problem. Think how you would go about doing your annual test for all the emerg lites?
 
Emergency lighting needs to be tested on a regular basis ie at least twice per year. The idea is to recyle the batteries, by discharging and recharging....So a maintenance agreement needs to be put forward here.....suggest reading BS5266
 
Ive only installed the systems, never really got involved in the maintenance but I thought the testing recommended in BS 5266 (2011) required a monthly function test to check that the emerg lite is working then an annual discharge test for the full duration of the emerg lite?
 
Ive only installed the systems, never really got involved in the maintenance but I thought the testing recommended in BS 5266 (2011) required a monthly function test to check that the emerg lite is working then an annual discharge test for the full duration of the emerg lite?

one a month quick function test, 6 months 30 minute discharge test annually full 3 hour test...all to be recorded into log book, by em number and location
 
Thanks chaps. Not involved with the maintenance of the rest of the EL, was just concerned with the testing of the one I've installed. Good idea Badge01, I'll do that. Got this job, whilst working nearby on another job, so perhaps regulat testing might be up for grabs. I'll need to read BS 5266 (2011)!
 