I am a retired electrician and have been out of the game for 10+ years but I now have to do some work on my campervan which has the requirement for double pole devices. Back in the day I would of happily used a two module RCD followed by a two module double pole MCB. However nowadays there appear to be plenty of compact, single module, double pole RCBOs available which look ideal given I am short of space. However then I started down a bit of a rabbit hole as I noticed they can either be marketed as double pole or 1P+N. If it was a MCB I can see the difference, double pole needs overload/fault detection on both Line and Neutral. However with say the MK H7732M, which is marketed as double pole, it looks like overload protection is only on the line (with RCD on both). Then the FuseBox RTAMB16B0 is marketed as 1P+N but appears to be the same configuration, ie overload detection on L but also switches the neutral.
Logically I cannot see why it would need neutral overload detection on an RCBO as L-E and N-E faults would trip on earth leakage and L-N overload on L overload detection.
Am I missing something, are these two devices actually the same and both meet the double pole requirement?

https://www.screwfix.com/p/mk-sentr...e-b-curve-bi-directional-miniature-rcbo/341ye

16A 30mA RCBO - Fusebox 6kA (Type A) B Curve (Compact) - Bi-directional | Fusebox (RTAMB16BD) - https://www.tlc-direct.co.uk/Products/FBRTAMB16BD.html?source=froogle&srsltid=AfmBOoq1xawJj1h-N9lWEU7cZiYSo1gRB6Kz13wQZkasz8y1JWCdumgwZM4
 
Scolmore's explanation last year:
1P&N – a device having a connection point for the line and neutral conductors (and followed by this perhaps outdated observation) typically taking up two ways on the distribution board. When the RCBO is switched on or off both the line and neutral conductor will open or close. However, the neutral connection will not have short-circuit capacity.

Which seems to be contradicted by the Fusebox spec of 6kA. Rabbit hole indeed!
 
The neutral will open on tripping/switching off with a 1P+N device. In that respect, no difference between that and a 2P device.

The difference comes with any supply where N isn't tied to E - such as when in a caravan and the supply is reversed for some reason, or running from a genny putting out 55-0-165V. In that situation, a N-E fault won't trip the MCB section of a 1P+N device.
You'd then be relying on the RCD section as the only protection, rather than just additional protection.
 
Yes, it is for a campervan I am concerned so reversed L-N is a potential issue. Are you saying relying on the RCD section for N-E fault protection is against the regs? So RCBOs like this would not meet the "double pole" requirements for campervans? I only have 17th edition regs but cannot find anything there.

I ask as this is the internal schematic for the MK "double pole RCBO", if I interpret it correctly there is no overload/fault detection on the neutral. Actually it doesn't show the RCD switching the netural either but it obviously does. Hence asking what makes this a "double pole" rather than "1P+N"?
20251010_092806.jpg
 
I've done a bit of digging and as far as I can tell it it all comes back to 721.43.1 which states "each final circuit shall be protected by an overcurrent device that disconnects all live conductors..." I had assumed that meant both line and neutral needed independant over-current protection and either would trip both. That would fit with Simon47's comments. However the MK RCBO doesn't show overcurrent/fault detection on the neutral. So I am wondering if it relies on the residual current detection to detect a neutral fault. But then I would expect a 1P+N RCBO to act in the same way.
 
Last edited by a moderator:
TBH, it's not an areas I've ever needed to look into, so I don't know if there's specifically a reg which would preclude using a 1P+N device where N might not be at (or close to) E - such as the reversed supply or genny supply situation I mentioned earlier. Overcurrent protection in the circuit will still work normally, but fault detection will work differently.

The issue is that there's no current detection in the N line. So if there's a N-E fault, then the MCB section won't detect it. So as I mentioned earlier, you are then relying on the RCD to provide the only protection rather than additional protection. I'll have to defer to others as to whether that's an issue regs wise.
 
Last edited by a moderator:
Thanks, yes, it does look like there is some ambiguity there though I am starting to think I am overthinking it. They are marketed as double pole, so should open both poles under short circuit conditions. Perhaps that is the only important distinction (as Avo Mk8 said) and how they do it is perhaps not so important. I suspect most sparks will just take the double pole bit at face value and sleep easy :)
 
The MCBs in my touring caravan are marked showing a current sensing element in both poles. I.e. two single pole MCBs bolted together with a linking handle.
Reversed polarity campsite supplies are very common in France.
 
The MCBs in my touring caravan are marked showing a current sensing element in both poles. I.e. two single pole MCBs bolted together with a linking handle.
Reversed polarity campsite supplies are very common in France.
Yes, traditionally I would do that but I am aiming for a much more compact system with single module RCBOs. Hence querying the capability of RCBOs.
 
721.415.1 Additional protection: RCDs - this Reg says that where ADS is used, you need a 30mA RCD "breaking all live conductors" - this suggests an RCBO with a switched neutral meets this requirement, whereas an RCBO with a solid neutral does not.

721.43.1 Final circuits - this says "Each final circuit shall be protected by an overcurrent protective device which disconnects all live conductors of that circuit." It does not say that there needs to be overcurrent detection on both live conductors, it just says that (a) there needs to be an overcurrent device, and (b) that this device needs to disconnect all live conductors (if an overcurrent is detected). This suggests an RCBO with a switched neutral meets this requirement.

Regarding earllier comments that in the event of reverse polarity, and relying on the RCD part of the RCBO in the event of a L-E fault (which, because of the reverse polarity, is actually N-E) then this is correct. I'd also note:

  • for TT systems, you rely on RCDs (or the RCD part of RCBOs) for fault protection, and this is quite normal, and permitted by the Regs - 411.5.2
  • as section 708 observes, the ESQCR prohibits the connection of a PME earthing facility to any metalwork in a leisure accommodation vehicle... in practice, this usually means TT.
 
Thanks, I was wondering if the latest regs had more detail than mine (2015) but it sound like they don't. Anyway, that does appear to cover it. As you say, if an RCD is good enough for TT fault detection then it should be good enough in the van.
 