Would you take it s a joke if I said it?

Seeing that you are The Muppet Police then you would arrest me if I didn't...
upload_2018-10-16_16-44-48.png
:)
 
This thread started off fine then but quickly turned into a chuckle brothers sketch (to you, to me) RIP Barry.

Did the op get an answer in the end?
 
To the op I think I know what you mean tails go into a isolator and then the wires go into the bottom of it , but now the wires are not double insulated and are out in the open . The earth side is not as much problem
 
To the op I think I know what you mean tails go into a isolator and then the wires go into the bottom of it , but now the wires are not double insulated and are out in the open . The earth side is not as much problem
Huh?
 
Hi, yes, MickFred, that’s why I have asked for any suggestions. Pme earthing arrangement, & cables have to travel within the wall to the Cu. Customer will not have any form of trunking.
 
This thread started off fine then but quickly turned into a chuckle brothers sketch (to you, to me) RIP Barry.

Did the op get an answer in the end?


My suggestion was in post #4. No reply as yet.
I'm very good at taking thread off at a tangent.. :)
 
Yes indeed the break out box is a possibility with a Henley maybe as per @ferg but getting those cables to behave in that confined space is something I would hate to take on. I assume we are talking 25mm².
 
If your swa is terminated into an external meter cabinet then you do not require your swa ‘tails’ to be double insulated when connecting to the DP isolator as the meter box is an enclosure, accessible with a key/tool only
 