The db came with a 4 pole isolator but I've been told it's ok to connect it straight to the neutral bar?
Surely this is bad practice?
If you’ve got a 4 pole isolator then use it.
Generally tho in a TN system you can use a 3 pole isolator to isolate the phases only,as the neutral is considered to be around the same potential as earth as they are connected together at the transformer/supply end.
TT 3 phase supply then the neutral needs to be isolated also.
Generally there’s a neutral terminal on the main switch with 3 pole type on some manufacturers types were the neutral connects but isn’t switched.

Domestic single phase consumer units tho require double pole isolation as used by ordinary persons or unskilled electrically or whatever the hell it is nowadays.
 
Last edited:
Doesn't matter the means of supply for a TN system, submain or the origin. Neutral is deemed to be at earth potential on TN systems and there is no requirement to isolate it. This is not the case for TT and isolation is required.
 
Never knew that and came across a UPS in a shop after the main 4 pole isolator was reset by staff in an attempt to reset a single rcbo.... interesting
 
As Lee says there can be good reason not to break the neutral for safety reasons. Obviously without knowing anything about the supply or Earthing arrangements etc. we cannot really advise in this instance. There simply hasn't been enough information.
 

Reply to Connecting the neutral directly to the neutral bar in the Commercial Electrical Advice area at ElectriciansForums.net

Similar Threads

I have breaker box at least 40 yrs old, both conduit and romex enter box, only one neutral bar that all white wires and bare ground wires attach...
Replies
4
Views
743
Hello, Looking for some advice following a botched 3 phase upgrade today. Some background: Commercial unit originally fitted out (4 years ago)...
Replies
7
Views
625
Recently started a retrofit where the 3 phase dB has been fitted with bushes through the galv trunking. The single phase supplies outgoing have...
Replies
1
Views
215
Hi all, Been a while since I have been on here. I have been on an apprenticeship the last 3 years training in the BMS world. Taking that into...
Replies
7
Views
343
Hi everyone, When checking my consumer unit voltages with the full board off, I stumbled across something head scratching. Measuring the feed...
Replies
1
Views
671

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock