Yes following tels advice get the Zdb then you can calculate the cable resistance and estimate zs before you wire it ... a larger cable may be needed if supply is good enough to start with.... alternately you can protect with hrc fusing which is not so harsh regarding zs values ..... if you don't pre-empt this before hand you may find your installs doesn't comply so heads up ... If you have a TNCS system and a good reading you may get away with a 6mm but still calc it ...next cable size up should cover you if its too close to call.

ok, maybe ill look into the hrc fuses, thanks
 
Update: Board Zs is 0.39! So that's type D out the window, at the mo I think its gotta be 32 type c, I don't really want unwanted tripping, Darkwood, where did you find the information you mentioned earlier about the MF's?
 
You can wire it in a smaller cable then and fit a 63(b) or (c) but still you have to consider the Zs allowance and yes you can have your mcb overate the cable due to the nature of the load been fixed this also needs calculating but can save your customer a bit of brass..... there's no quick answer here it all involves working it all out ..... Check regs for BS88 fuses otherwise and notice how much more leeway you have
 
You can wire it in a smaller cable then and fit a 63(b) or (c) but still you have to consider the Zs allowance and yes you can have your mcb overate the cable due to the nature of the load been fixed this also needs calculating but can save your customer a bit of brass..... there's no quick answer here it all involves working it all out ..... Check regs for BS88 fuses otherwise and notice how much more leeway you have

Thanks for the reply, Ive quoted it for a 10mm cable now, are you saying that because its fixed equipment I can de-rate the cable? Ive never come across that before, can you you point me to the relevant regs? thanks
 
Look up regs for overload protection and look at when its acceptable to omit overload protection of the cable .. you need an understanding of the equipment to use this clause but a quick scenario would be a pump thats fed by a dedicated supply and has overload protection within the controls ... if you have issues with mcb tripping on start up you can increase the size of the mcb past CCC of cable as long as it still complies with Zs for short circuit protection...

You can even have a mcb overate the cable in a domestic shower as long as the load demand is less than the ccc of the cable and zs complies .... although domestic isn't really an area to use this regulation but it can be and still be in compliance.

Its not a regulation to be utilised freely you need to have good knowledge when and where this reg can be used and within industrial it can save alot of money on cable.
 
Look up regs for overload protection and look at when its acceptable to omit overload protection of the cable .. you need an understanding of the equipment to use this clause but a quick scenario would be a pump thats fed by a dedicated supply and has overload protection within the controls ... if you have issues with mcb tripping on start up you can increase the size of the mcb past CCC of cable as long as it still complies with Zs for short circuit protection...

You can even have a mcb overate the cable in a domestic shower as long as the load demand is less than the ccc of the cable and zs complies .... although domestic isn't really an area to use this regulation but it can be and still be in compliance.

Its not a regulation to be utilised freely you need to have good knowledge when and where this reg can be used and within industrial it can save alot of money on cable.

This isn't a fixed load
 
This isn't a fixed load

Define a fixed load ... with regards to the regs...

It applies to obvious fixed loads like elements and variable loads like machine where you have a plated load on the machine which specifies the max loading of the machine, this can be taken as a fixed load but the characteristics of the machine/control system must be taken into account if you are to do so.

A control system or motor etc with its own overload protection can be thus classed as a fixed load regardless of its variable demand all you look at is max demand.

Although we shouldn't really consider applying this reg's to domestic other than the ring main most house circuits can be 'if designed correctly' be classed as fixed load circuits and thus the mcb can be rated higher than the ccc of the cable if zs is in compliance ... the reason we generally don't is that domestic is too easily the victim of DIY, adaptions, alterations etc by non competent people... ironically the IET give a shower scenario as an example of utilising this regulation.
 
Define a fixed load ... with regards to the regs...

A load which can not vary, so fixed, a resistive load.

It applies to obvious fixed loads like elements and variable loads like machine where you have a plated load on the machine which specifies the max loading of the machine, this can be taken as a fixed load but the characteristics of the machine/control system must be taken into account if you are to do so.

A control system or motor etc with its own overload protection can be thus classed as a fixed load regardless of its variable demand all you look at is max demand.

Well if the machine has a built in overload protection this can be used to protect machine and cable, so upstream device needs only to protect against fault current. Without overload protection at the machine, whats to protect the windings etc and the cable from thermal damage?

Although we shouldn't really consider applying this reg's to domestic other than the ring main most house circuits can be 'if designed correctly' be classed as fixed load circuits and thus the mcb can be rated higher than the ccc of the cable if zs is in compliance ... the reason we generally don't is that domestic is too easily the victim of DIY, adaptions, alterations etc by non competent people... ironically the IET give a shower scenario as an example of utilising this regulation.

A shower is a fixed load, how could it cause an overload, there is no mechanical losses like there is in a motor?

The OP is discussing protection for the cable, so we have a load which can create overload condition's, does the hoist provide protection for windings, if so this in effect protects the cable from overload as the protection is normally 1.1 - 1.2 FLC. The Upstream CPD then only need to provide fault current protection.
 
The OP is discussing protection for the cable, so we have a load which can create overload condition's, does the hoist provide protection for windings, if so this in effect protects the cable from overload as the protection is normally 1.1 - 1.2 FLC. The Upstream CPD then only need to provide fault current protection.[/QUOTE]


From what i've read so far, this is what darkwood is talking about...
 
ENG54 is getting my approach i think chris you are going off on a tangent to what i actually meant.

If a control system is variable load but has its own protection from overload either by the nature of its design or by fused/overload protection within the system then you can utilise the reg' regarding fixed equipment and negate the need to protect the supply cable, as long as Zs is still in compliance and the cable can meet the max load the equipment it supplies needs then this is ok....

Regulation 433.3.1 (ii) was the one i was highlighting to the OP although he will have to assess whether this situe' would be suitable to use this reg... either way he's gone for a 10mm cable now so this is just theoretical banter now.

Id already expressed using other types of OCPD to give higher Zs permitted values
Id expressed the chances of nuisance tripping with his choice of mcb 32 (c) -- this is why i brought up the options of omitting O/L protection on the supply in case he tried it and it tripped, if he thought his cable size choice might stop him upgrading the MCB to suit then i was merely saying if the controls are sufficiently protected then there is an option to just uprate the mcb passed the ccc of the supply cable he chose.

We lack info of the install and equipment to say yes you can do this but it gives an insight that this option maybe available to him if he has nuisance tripping of which he can return and ask for more info....
 
Update: Board Zs is 0.39! So that's type D out the window, at the mo I think its gotta be 32 type c, I don't really want unwanted tripping, Darkwood, where did you find the information you mentioned earlier about the MF's?

Are you using the correct tables?
Tripping time would be 0.2 seconds if this is site based.

Boydy
 