Cpc is there mate, was originally a permanent trip on the rcd, but now it's just the mcb going. It's fine while I'm there, then I get a phone call a few hours later to find its gone. The faults there are odd and seem to come and go which isn't helping things. Nor is the fairly that it's in Crawley and I'm on the edge of SW London!
 
anything on timers?

or when anyone is moving around?

or maybe when someone has a shower...or just after having a shower...or emptying the bath?
 
has kev kitchen caught a cable with a screw?...and it moves slightly when someone leans on one of the units...or worktop?...
 
Not as far as I know, but it's not always easy getting information out of people, especially the elderly. Last time I had a fault with the mcb going this way, it was a downstairs lighting cable trapped between a heating pipe and the upstairs floor boards. All laminate flooring upstairs though so I would hope it's not something similar!
 
has kev kitchen caught a cable with a screw?...and it moves slightly when someone leans on one of the units...or worktop?...

Already found one screw through a cable (wall unit feeding socket which dishwasher uses but that's isolated, well one of the cables is), the worktop is a very good point though because it's going quite often when people are in the kitchen.

Just one of those hard situations where I keep leaving with it working, and it then goes again.
 
Already found one screw through a cable (wall unit feeding socket which dishwasher uses but that's isolated, well one of the cables is), the worktop is a very good point though because it's going quite often when people are in the kitchen.

Just one of those hard situations where I keep leaving with it working, and it then goes again.
OK...
well theres your first clue then...

so...now we start to narrow it down....
if it were me i would be having a lean & tug on them units...and the worktop...
have a good tramp about on the floor as well...
 
kev kitchen has already demonstrated what a dummy he is....
you can bet it`l be something he has done....
 
Not as far as I know, but it's not always easy getting information out of people, especially the elderly. Last time I had a fault with the mcb going this way, it was a downstairs lighting cable trapped between a heating pipe and the upstairs floor boards. All laminate flooring upstairs though so I would hope it's not something similar!
so it aint just kev then is it...

seems like auld wetpants has put in an appearance as well...
 
OK...
well theres your first clue then...

so...now we start to narrow it down....
if it were me i would be having a lean & tug on them units...and the worktop...
have a good tramp about on the floor as well...

The kitchen and the immersion heater cupboard above are the two areas I'm concentrating on. That's where the faults seem to keep appearing. I'll no doubt find a couple more next time I search, hopefully one of those will be the final one.
 
The kitchen and the immersion heater cupboard above are the two areas I'm concentrating on. That's where the faults seem to keep appearing. I'll no doubt find a couple more next time I search, hopefully one of those will be the final one.
just IR test between the pipework and the neutral....
 
Trying to post a picture but it won't let me, I found a nice melted cable behind a sink that someone had taped up in the past.
 