Anybody got any advise on what would be the best way fitting a new consumer unit with a timer for storage heaters,
would appreciate hearing any pearls of wisdom.
 
Probably using a contactor controlled by a timer to control the consumer unit? Or i have seen timer type MCB's that can control the circuits in question?
Is the current installation eco7 or standard?
 
Consumer unit with mcb's for storage heaters, run these circuits through contactor(s) run the control circuit of the contactors through a time switch.

Timers normally can't carry the load of storage heaters.
 
It may be cheaper to get the tarrif changed to an eco 7 or even a off peak supply put in then you could connect the immersion to it as well
 
as oldtimer said, get in touch with your provider regarding changing tarrifs to eco 7 or 10. They will fit a timer for you to power a seperate board.
 