Feb 19, 2019
24
South Wales
Business Name
Gold Electrical and Security
Job is to upgrade consumer unit with RCBO's unit, upgrade tails to 25mm tails, 16 mm main earth, 10mm to Gas, however cant get to water pipe / water stop existing bonding is 4 or 6mm all concealed behind tilled wall, system. any advice
What is the earthing system.
Are the incoming supply pipes plastic or metallic?
I had a similar case recently.
I managed to cut out a tile with a disk without hitting the water pipe and then had enough room to use old conductor to pull through a new one. It was a happy day - I even got the tile back without breaking it!
If that isn't possible, and it is extraneous, I'd prefer to be running a new 10mm to wherever I can get to (literally interpreting "as near as practicable to the point of entry") bearing in mind someone else might need to find it one day.
I recognise that if not PME you could go on a paper trail to see if you can justify the current bonding csa. While not wrong I don't think I'd do that myself as I don't really want to be downsizing a main earthing conductor to solve a bonding problem.
If you can check with a wander lead that the stop-cock is well-connected (e.g. bond resistance 0.05 ohms or so) then it comes down to if it is TN-C-S and merits 10mm instead of the 4/6mm.
I presume the water pipe entry / stop-cock is accessible?
South Wales
Business Name
Consumer unit upgrade
Jeremy Hale,
pc1966,