Peter Woodford

Could you tell me when installing a fuse board to meet the 17th edition regs does your consumer unit have to be spilt load i.e 2no rcd breakers. Was going to install split board one side with main isolator other with 1No rcd so that not everything trips on one side.Hope you understand this


cheers


Pete
 
Peter,

Basically yes, all circuits SHOULD be RCD protected, so you could install a standard split load board, but the unprotected circuits would need to have an RCBO in place of a standard MCB.

This can work out fairly expensive so a 17th Dual RCD board is the best way to go.
 
hi
i think u can as long as u get departures from client, but dont think spilt board complies,,, sure someone will tell u if i am wrong

hi
again, knew i was wrong
 
Last edited by a moderator:
Peter,

Basically yes, all circuits SHOULD be RCD protected, so you could install a standard split load board, but the unprotected circuits would need to have an RCBO in place of a standard MCB.

This can work out fairly expensive so a 17th Dual RCD board is the best way to go.

Is it not possible to have a named circuit before the 2 splits that is not rcd protected ( as long as it does not contravene other regs like buried less than 50 mm )eg a freezer radial, so that it does not suffer nuisance tripping?
 
Yes you can but as you have said, as long as it does not go against other regs and is clearly labeled it can be left off RCD protection.
 

Reply to consumer units in the Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock