at the minute any problems, nuisance tripping with that and the whole installation goes offWhat's the reason for getting rid of the 100mA RCD ?
at the minute any problems, nuisance tripping with that and the whole installation goes offWhat's the reason for getting rid of the 100mA RCD ?
at the minute any problems, nuisance tripping with that and the whole installation goes off
because it will comply when he makes out the cert. sod next year.What would be the point of making any changes to the distribution board, since in four months time, it wouldn’t comply again?
What would be the point of making any changes to the distribution board, since in four months time, it wouldn’t comply again?
forgive my ignorance but what will be happening in four months time?What would be the point of making any changes to the distribution board, since in four months time, it wouldn’t comply again?
ha ha, i was aware about the consumer unit changesNew years eve pi$$ up, followed by heavy metal CUs.
.
SPSN = Single Pole Solid Neutral, NOT Single Pole Switched Neutral.
Done a little research and read that 100ma time delayed rcd acting as a main switch on a TT system is no longer required providing that all circuits are 30ma protected and the DB is of an all insulated material
i would be installing a 30ma rcd to protect the lighting curcuits currently protected by a 100ma rcd. Does this make the system any less safe? Removing the 100ma rcd and replacing with a main switch would also allow the installation to be divided better so in the event of a single fault the whole installation would not be lostat the minute any problems, nuisance tripping with that and the whole installation goes off
But removing it removes the backup fault protection it provides when the 30mA fails to trip.
By removing it you are making the installation less safe than when you found it.