at the minute any problems, nuisance tripping with that and the whole installation goes off

But removing it removes the backup fault protection it provides when the 30mA fails to trip.
By removing it you are making the installation less safe than when you found it.
 
RCBO all the way, in my book. keep trhe spare RCD for another job.
 
What would be the point of making any changes to the distribution board, since in four months time, it wouldn’t comply again?
 
What would be the point of making any changes to the distribution board, since in four months time, it wouldn’t comply again?
because it will comply when he makes out the cert. sod next year.
 
Wylex NHXSBS type RCBO is single pole solid neutral not switched, as are 90+% of those in the market place.
There are VERY, VERY few double pole or single pole switched neutral RCBO's.
SPSN = Single Pole Solid Neutral, NOT Single Pole Switched Neutral.
 
What would be the point of making any changes to the distribution board, since in four months time, it wouldn’t comply again?


It will comply exactly the same in years time as it does right now, he is on about swappong a RCD for a main switch not swappping the whole DB.
 
New years eve pi$$ up, followed by heavy metal CUs.
 
Done a little research and read that 100ma time delayed rcd acting as a main switch on a TT system is no longer required providing that all circuits are 30ma protected and the DB is of an all insulated material
 
Ok, I've skip read and drunk the best part of a bottle of wine but something doesn't bode well with the op's questions
 
Done a little research and read that 100ma time delayed rcd acting as a main switch on a TT system is no longer required providing that all circuits are 30ma protected and the DB is of an all insulated material

But if it's there already why remove it? You will only be removing an additional layer of protectection
 
at the minute any problems, nuisance tripping with that and the whole installation goes off

But removing it removes the backup fault protection it provides when the 30mA fails to trip.
By removing it you are making the installation less safe than when you found it.
i would be installing a 30ma rcd to protect the lighting curcuits currently protected by a 100ma rcd. Does this make the system any less safe? Removing the 100ma rcd and replacing with a main switch would also allow the installation to be divided better so in the event of a single fault the whole installation would not be lost
 