Been to look at a job and the customers consumer unit is split load 100a 100ma time delay rcd, which is acting as the main switch and 80a 30ma rcd. Upstairs and downstairs lights are protected via the 100ma rcd, with the rest of the installation via the 30ma. Ive been asked to do some work on the upstairs lighting circuit including in the bathroom. What i want to do is remove the 100ma rcd and replace it with a 100a double pole main switch and then install an additional 80a double pole rcd.
Obviously i am going to use up an extra two ways in the board, but there is the capacity to do this. Just wondered if i would need to buy any extra kit, additional bus bar or maybe links to feed the new rcd?