i would be installing a 30ma rcd to protect the lighting curcuits currently protected by a 100ma rcd. Does this make the system any less safe? Removing the 100ma rcd and replacing with a main switch would also allow the installation to be divided better so in the event of a single fault the whole installation would not be lost
Yes it makes it less safe, the 100mA RCD would provide a second level of fault protection if left in place. Being time delayed it will only trip if the 30mA RCD fails to trip due to being faulty.
If the 30mA RCD works correctly then the 100mA RCD will not trip