Tri-rated cable is designed to run at a higher temperature than standard PVC flex, and should only be used at that rating when connected to switchgear also designed to run at high temperature. We have the same issue when using XLPE swa...just because the cable can run hotter, it doesn't mean that it should.
and any encosures its glanded off into should also be rated for the tempratures likely/expected...
 
here's an enclosure yorkshire men will like.

sheep.jpeg
 
Woman says it was supplied like this


What woman?? Saleswoman, ...do we really take notice and believe all that a salesperson tells us now?? lol!!

I doubt very much that this free standing all in one cooker has been manufacture supplied with a 1.5mm or 2.5 mm cable
 