4mm² will do with 32Amcb and method C.

Just to be extra safe - don't have a socket in the cooker switch.
 
4mm² will do with 32Amcb and method C.

Just to be extra safe - don't have a socket in the cooker switch.

above statement obviously a wind up , 11.5kw will pull around 50 amps

you will need 10mm on 50a breaker
 
cobblers. 6mm on a B32, good for any bloody cooker. (up to 15kWatts). look it up.
 
New Supply id run 10mm.. However domestic setting using divercity it will be lucky to pull 32a.. Existing supply then use a commen sence aproach and well make sure its fueed accordingly subject to refereance method...
 
dave, your spellings atrocious. have another beer.
 
New Supply id run 10mm.. However domestic setting using divercity it will be lucky to pull 32a.. Existing supply then use a commen sence aproach and well make sure its fueed accordingly subject to refereance method...

divercity............is that where Drogba and Ronaldo live?
 