what if it's 500 mtrs away from the dist board jeff?
geroff!!! 500m from DB to kitchen in a domestic. it ain't buck house.
what if it's 500 mtrs away from the dist board jeff?
11500w cooker 6mm or 10mm?? Mmmm??

Thanks for info guys![]()
above statement obviously a wind up , 11.5kw will pull around 50 amps
you will need 10mm on 50a breaker
gawd 'elp us.
it might wel protect the cable, but it won't protect his wallet. 10mm for a poxy cooker? what's next? 25mm for the shower?