Davem
Hi guys hob rated at a max load of 6kw so with diversity implemented the mcb should be 20 amp right seems a bit low to me for a cooking outlet but is this right ?
Depends. Is there a socket outlet on the cooker switch plate or not?
20A is lower than generally seen. The question is what is the rating of the installed cable allowing for its size and worst case reference method?
I hate flipping cooker diversity. Here we are, placed at great pains to avoid anything that could cause overload, and then the diversity calculation basically says "Overload? Bring it on". Always strikes me as a recipe for a blown fuse at lunchtime on Christmas Day if you're lucky, and a housefire if you're not.
Don't want to limit the mcb just want to ensure its safe. I used 6mm and that will allow 34amps. So either a 20 or 32 amp will protect the cable but will a 20 cause nuisance tripping as it is on boarder line ?
size the MCB to the cable. in this case 32A ( or 40A if ref. method C ) . end of.
I'm not following your logic but maybe that's because I'm old, tired and poorly but why the **** do you want to confuse yourself with over thinking such a simple thing??
You say the cable is happy to carry 34 amps so why not just shove a 32 amp protective device in?? What in God's name made you even consider a 20 amps breaker???
Did Dan send you??
Thanks guys relatively new and my assessment is next week and like u say I am over thinking things and totally confusing simple things cheers
Ib<In<Iz should make it clear.
32 amp to save a lot of hassle so,e bright spark at my mates company thought it was a good idea to run 10mm for cookers :6: