Hi guys hob rated at a max load of 6kw so with diversity implemented the mcb should be 20 amp right seems a bit low to me for a cooking outlet but is this right ?
What size cable is/have you installed??Yes why
Don't want to limit the mcb just want to ensure its safe. I used 6mm and that will allow 34amps. So either a 20 or 32 amp will protect the cable but will a 20 cause nuisance tripping as it is on boarder line ?
Ib<In<Iz should make it clear.
This Dan fella has a lot to answer for ......