nickblake

Ok just wanted your opinion 2.5mm flex provided by the supplier on cookers and hobs , ive seen this twice and in my eye its wrong a hob of 7 kw and a slide in cooker of 7500 kw , it realy makes a mock of calculating cable sizes , ok if you take diversity into effect max current rating of flex is 25 amps ish diversity loading will be about 19 amps so all ok , well all untill you get a fault that is and the cable melts just wondering what your thoughts were , oh on both ive changed them to 6mm flex
 
Ok just wanted your opinion 2.5mm flex provided by the supplier on cookers and hobs , ive seen this twice and in my eye its wrong a hob of 7 kw and a slide in cooker of 7500 kw , it realy makes a mock of calculating cable sizes , ok if you take diversity into effect max current rating of flex is 25 amps ish diversity loading will be about 19 amps so all ok , well all untill you get a fault that is and the cable melts just wondering what your thoughts were , oh on both ive changed them to 6mm flex
well as you know nick.....a fault of neglegable impedence will take out the OPD or RCD/RCBO anyway.....so i dont get your drift?...
 
Nick where did you get 6mm flex locally?, CEF do 4mm that's what I do my hobs in

Get it from senet mate H05 6mm great stuff , funnily enough cant get 4mm in bangor

yes will trip the rcd etc to much reliance is put on RCD's these days , realistically speaking hobs and cookers can be on for long periods of time and you cant tell me they are not all used at the same time , i use all mine cooking sunday lunch and both ovens , see it to often on showers burning out and not tripping the RCD or mcb just catching fire no differance on cookers same sort of loading and possible on for longer durations ,
 
Cheers nick I now know where to go for it!, can get 4mm in CEF Llandudno but I've stop dealing with them now, it's Network in Mochdre or Electric fix for me!
 
Ok just wanted your opinion 2.5mm flex provided by the supplier on cookers and hobs , ive seen this twice and in my eye its wrong a hob of 7 kw and a slide in cooker of 7500 kw , it realy makes a mock of calculating cable sizes , ok if you take diversity into effect max current rating of flex is 25 amps ish diversity loading will be about 19 amps so all ok , well all untill you get a fault that is and the cable melts just wondering what your thoughts were , oh on both ive changed them to 6mm flex

Are you saying that the manufactures don't know what cable size/type to provide for the appliances they are producing and selling to the general public??
 
Ok just wanted your opinion 2.5mm flex provided by the supplier on cookers and hobs , ive seen this twice and in my eye its wrong a hob of 7 kw and a slide in cooker of 7500 kw That's one hell of an oven! :-)
, it realy makes a mock of calculating cable sizes , ok if you take diversity into effect max current rating of flex is 25 amps ish diversity loading will be about 19 amps so all ok , well all untill you get a fault that is and the cable melts just wondering what your thoughts were , oh on both ive changed them to 6mm flex

So what happens to the fixed cct wiring in the event of a fault when there's several 100 Amps flowing?
 
Last edited by a moderator:

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Cookers Hobs wired in 2.5mm flex
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
9
Unsolved
--

Advert

Thread statistics

Created
nickblake,
Last reply from
Silly Sausage,
Replies
9
Views
13,028

Advert

Back
Top