Most of the spec online state that separate terminal will take a 16.0.
Yes exactly, I wonder how many people have installed one thinking the enclosure is linked to itI noticed that in pictures of it. I really wonder why they have the switch CPC terminal at all, why not have just the box adequately sized?
No that’s the earth terminal joined to the switch , the three connection are L N EMost of the spec online state that separate terminal will take a 16.0.
Tails in swa outIs it swa in and out or tails in.
Could you just take the 16mm CPC to a crimp lug bolted to the SWA's banjo and, assuming 3C SWA, also put a lug on the cable's SWA conductor to the same bolt?Tails in swa out
Stick another 10.0 in for the terminal if it fits.Tails in swa out
Yes I think that is the only option, it’s a lot of extra faff and the switches are not cheapCould you just take the 16mm CPC to a crimp lug bolted to the SWA's banjo and, assuming 3C SWA, also put a lug on the cable's SWA conductor to the same bolt?
i.e. Ignore the switch's through-CPC connection and the box's terminal strip completely.
EDIT: Also you could use a nylock nut if concerned about it coming loose.
No only takes a 10 mmStick another 10.0 in for the terminal if it fits.
Sorry I ment only takes a 16mmNo only takes a 10 mm
Could you knock the existing small terminal block off the box and fix something like this in its place with a pair of machine screws:Yes I think that is the only option, it’s a lot of extra faff and the switches are not cheap
What size cpc should I earth banjo with?Sorry I ment only takes a 16mm
Depends on the fuse I guess. The On-Site Guide table B4 & B5 has smallest CPCs meeting adiabatic limit for fuse and Zs cases.What size cpc should I earth banjo with?
So this separate terminal will take a 16.0?Sorry I ment only takes a 16mm
That’s a good option it’s a shame I have fifteen to do of theseCould you knock the existing small terminal block off the box and fix something like this in its place with a pair of machine screws:
![]()
CED 4-Way Earth Block - Screwfix
Order online at Screwfix.com. Nickel-plated. FREE next day delivery available, free collection in 1 minute.www.screwfix.com
You might need to have nuts on top and use countersunk heads coming through from the back to is fixes flush though.
It will be a 80amp hrs, have seperate cpc so not relying on the armouredDepends on the fuse I guess. The On-Site Guide table B5 has smallest CPCs meeting adiabatic limit for fuse and Zs cases.
Sorry no on the switch L and N will take up to 35mm and earth takes 16mm maxSo this separate terminal will take a 16.0?
What size cpc should I earth banjo with?