I asked for the minimum word count in case people wanted to call me a w4nk3r,

now they still can, but they have to explain themselves a little more to inconvenience themselves!! 😉😉😉
 
Last edited:
Kudos to you guys knowing it was an RCD without even looking 👏 I feel foolish not realising rcds were built in to the main isolator on boards like this.
In my defense the board is at the bottom of a tight cupboard and the writing on it is very small 😅

So to clarify, it's the rcd tripping occasionally when the shower is/has been running.

Turning off the ring supplying the kitchen/bedroom will allow the rcd to come back on but that ring has to stay off for a good 30mins to an hour before it'll come back on without the rcd tripping again

The mcbs aren't labelled properly since the ring supplying the kitchen/bedroom is actually the one labelled 'spare' and the 32a mcb 4th from the right is the spare, which suggests they've been swapped over at some point right? Probably due to this fault?
 

Attachments

  • 20220914_183234.jpg
    20220914_183234.jpg
    353.1 KB · Views: 94
  • 20220914_183255.jpg
    20220914_183255.jpg
    240.6 KB · Views: 76
  • 20220914_183258.jpg
    20220914_183258.jpg
    234.4 KB · Views: 82
Kudos to you guys knowing it was an RCD without even looking 👏 I feel foolish not realising rcds were built in to the main isolator on boards like this.
In my defense the board is at the bottom of a tight cupboard and the writing on it is very small 😅

So to clarify, it's the rcd tripping occasionally when the shower is/has been running.
If it is always shower-related then the above advice to look for water leaks is an important starting point to be checked/fixed before anything else.
Turning off the ring supplying the kitchen/bedroom will allow the rcd to come back on but that ring has to stay off for a good 30mins to an hour before it'll come back on without the rcd tripping again
That strongly suggests it is a socket or junction box related to that circuit that is getting wet.
The mcbs aren't labelled properly since the ring supplying the kitchen/bedroom is actually the one labelled 'spare' and the 32a mcb 4th from the right is the spare, which suggests they've been swapped over at some point right? Probably due to this fault?
More likely that the kitchen had some work done an an additional circuit put in, etc.

That is a very old board! Good to see the RCD is still working though, but at some point you ought to consider replacing it, maybe as part of a supervised assessment as your training progresses?

Again, if I were you I would be looking to determine exactly what circuits are in use and check everything out. Did you get an EICR as part of the documents for your new home?
 
Again, if I were you I would be looking to determine exactly what circuits are in use and check everything out. Did you get an EICR as part of the documents for your new home?

No we didn't, the previous owner had the property around 8 years and stated in the documents no electrical work had been carried out during their time there.

By the look of the shower isolator in the landing cupboard it was installed as a DIY job
 

Attachments

  • received_2060353810815813.jpeg
    received_2060353810815813.jpeg
    49.5 KB · Views: 103
By the look of the shower isolator in the landing cupboard it was installed as a DIY job
Could be that he just forgot to bring the large T&E cable clips that day.
At least you have a decent quality isolator that's up to the job, rather than one of those totally inadequate pull cord efforts.
 