- Reaction score
- 148
Hi guys, I expect this topic has been covered before, In rented accommodation including business premises, should the electrical installation be up to current BS 7671 Regulations.
Discuss Current 18th Edition Compliance in the UK Electrical Forum area at ElectriciansForums.net
The installation should comply with the regs that were in force when the wiring was done. IF it complied then, and hasn't deteriorated or become damaged in the meantime, then, with a very few exceptions, it complies now, although deviations from the current regs will attract a C3 classification on an EICR.
Thanks for your replies. I find it a little confusing as according to the Government website Quote :
What standard should the electrical installation meet?
The standards that should be met are set out in the 18th edition of the Wiring Regulations.
The Regulations state that a landlord must ensure that electrical safety standards are met and that investigative or remedial work is carried out if the report requires this.
The electrical installation should be safe for continued use. In practice, if the report does not require investigative or remedial work, the landlord will not be required to carry out any further work.
It then goes on to say :
Existing installations that have been installed in accordance with earlier editions of the Wiring Regulations may not comply with the 18th edition in every respect. This does not necessarily mean that they are unsafe for continued use or require upgrading.
Depends on the situation, if this represents a danger, for example a socket outlet used for lawnmowers - that is equipment outside, then most would code this as a C2, if a second floor room or flat, then C3 (as it can't be used for outside equipment), ground floor which may be used for equipment outside - some would say C2, some C3 depending upon how likely the use of outside equipment is.So if you do not have rcd protection on socket outlets it is only a code 3.
More like £1000+ a month the way it's heading at the moment.The Best Practice Guide #4 on EICR is probably your best starting position on deciding if an installation is acceptably safe or not:
However, if it is rented out (i.e. commercial use) I would be less forgiving of issues like lack of RCD protection where any chance of outdoor use, etc, is involved. After all, if the owner is getting £500+ per month then it is hard to see them not being able to afford that sort of issue being addressed, and they are not the ones being put in any personal danger.Best Practice Guides | Electrical Safety First
Electrical Safety First produces, in association with other industry bodies, a range of Best Practice Guides which provide definitive information and guidance on a range of technical subjects.www.electricalsafetyfirst.org.uk
No, the risk assessment omission of RCD has, AFAIK, been removed in Amd2. Whether or not you can use other protective measures in its place would be down to the design.So in a commercial setting with no rcd protection on socket outlets, will a risk assessment on an outlet not more than 32A that could be used outside get you out of jail ?
Reply to Current 18th Edition Compliance in the UK Electrical Forum area at ElectriciansForums.net