Can anyone help me out with this? Need to find the max current carrying capacity for 4mm singles over a 10m length in both metal trunking/pipe with a 20A 60898 B Type breaker protecting cct. No thermal insulation at an ambient temp of 30•C.

If anyone can help with breakdown of calculations with equation that would be great.

Many thanks.
 
Is this a real life situation or a theoretical one?
Or to put it another way are you asking us to do your homework for you?
Or are you an electrician who doesn't know how to do this?
 
start with the 20A MCB. multiply this by 30deg. ambient temp., then use the formula F = 9/5C -32, and that's your answer. :stupid:
 
Can anyone help me out with this? Need to find the max current carrying capacity for 4mm singles over a 10m length in both metal trunking/pipe with a 20A 60898 B Type breaker protecting cct. No thermal insulation at an ambient temp of 30•C.

If anyone can help with breakdown of calculations with equation that would be great.

Many thanks.
Start with the table 4D1A in BS7671.
Check the number of live conductors, installation reference method and ambient temperature.
Apply any corrections required for any other limitations and you will have your answer.
 
I hope it was a homework question and not someone who is actually doing this for a living!
 
Cheers Richard, that's the method Iv followed. Was just making sure I wasn't missing anything, turned out I was missing the time characteristics. But all sorted now, thanks for your sensible input.
 