Oct 17, 2023
28
Hampshire
Trainee Electrician
Having a challenge understanding the concept behind why when you measure across line and neutral (live circuit) using voltage indicators we have voltage reading of 230V single phase. If there is current flow in the neutral why is it termed as 0V ?
On that basis, second question - If I tested across Neutral and Earth, there is current flow down the neutral back to the transformer, why would the tester show 0V ?
Strictly speaking it is the true Earth (i.e. our planet) that defines zero volts. All voltages are a relative measure (i.e. a potential difference between two electrodes), but once you define a known and world-wide point as 0V you have the means for absolute measurement.
Neutral is defined on the basis that it is referenced to Earth, where as the other line conductors are not. All of L1-L3, N are "live" as they are current-carrying, so if you have an open fault on N then the load-end becomes dangerous indeed.
It depends on three factors:
  • How much current is flowing
  • The N cable impedance to the N-E link
  • The resolution of you meter
If your meter only measures in steps of 1V then you might be seeing 0.4V and it reports zero. If you have a TN-C-S system then the N-E link is at the supply point (DNO cutout) so the impedance of the neutral cable could be small as it is quite short, etc.
This PDF document from the IET has some useful illustrations of typical earthing arrangements:
https://electrical.----------/media/1698/earthing-your-questions-answered.pdf
Im struggling to grasp the concept in an AC generator at opposite sides of the generator one side becomes positively charged the other side becomes negatively charged. Then we add a cable to both ends and as the core/ shaft spins within a generator this current changes direction back and forth back and forth, and so on to give us AC electricity. But then when the power comes into a domestic property it’s only on the line conductor that I have amps coming into the property ? Using the explanation of how the generator works I’m stuck in my head trying to work out why it isn’t coming in on the phase, then coming in on the neutral and then on the phase and so on. Any help would really be appreciated guys . Thankyou for the responses so far
@Rob678 - welcome to the world of Yr 1 college theory?? The reason I'm asking is because we'll all absolutely help you, learning and sharing/teaching knowledge is a beautiful thing, it just helps us tailor our replies and point you towards suitable other resources.
Reactions: Rob678
That's the only bit of your last post that isn't quite right! Why do you think that?
The (equal) current that 'comes in' on the live, as you nicely put it, 'goes out' on the neutral. And as it's AC, half of the time it's 'coming in' on the neutral!
If you care to put a clamp ammeter on first the L and then the N tail of a consumer unit you will see the same current flowing in each.
I think you might have got confused about voltage vs current from what you said in your first post, maybe because the N is attached to ground as previously explained.
But your narrative in post 4 is basically correct 🏅
Hi Rocking it, yes first year at college for me. Thankyou for the help.
Thankyou Avo for your response. To be honest from reading some information online and a few early lessons at college, in the most basic form. If I imagine myself as a generator and I hold a rope in each hand around a tree. If I pull with my left the opposite must happen on my right and visa versa. If I stopped and then inspected the rope where it was touching the tree. The abrasive marks / heat produced by rubbing against the tree can be attributed to the current flow with a load attached. This is how I determine AC (in a very basic form) but some of the guys who I’ve spoke to at work only see it from the view power comes in on the live and leaves on the neutral. And I just feel like that’s theoretically incorrect based on the curious research I’ve done so far.
Thanks for your thoughts. I am interested to know about your 'curious research'!
Terminology is important. 'Power' in slang is often used to describe the presence of a voltage, but its meaning is more akin to 'energy'. In electrical terms, power is current x voltage = Watts. To be pedantic 'power' does not 'go out' of the neutral. It is given up in the load being fed, and during this process current flows in both live and neutral (even that's a simplification of course, electrons bounce around, rather than 'flowing' en mass, but that's a whole other story!)
Your rope around a tree analogy generating heat works if you think of the distance moved by the rope as current, and tension in the rope as voltage. If you ignore the elasticity of the rope and change in dimensions of the tree (!), then the distance you pull the rope on one side is the same as the movement on the other. But the work you put into the pulling, (force x distance), is absorbed by friction at the tree, and if you were to measure the tension at the loose end of the rope, it will be less due to the tree absorbing some. At the extreme limit where the tree friction absorbs all your pulling, there is no tension on the far end of the rope, equivalent to no voltage on your neutral wire, and the scenario you describe in your first post, asking why the tester shows 0V on the neutral wire. But there is current flowing (movement of the rope). Yeah that's contrived, but go with the flow 🤫.
Bearing in mind you are pulling alternately on each rope 50 times a second 🤪
Does that work for you?
PS not everything you read online is true (particularly on Quora 🤔)
I think to generate that frequency a lot more physical training would need to be done by myself !! Most of the research I’ve conducted on my own has been through speaking to work colleagues, reading some text books and looking into forums e.g. this one. I don’t know if I’m just really missing a really simple point I’m just struggling to see the points a little bit still. I’ve been having a look at some diagrams and I feel I’m getting there a little bit.
Cables run from the Generator to a step down transformer.
Am I right in saying from the generator to the transformers we don’t need a neutral ? Because as one phase is at a maximum positive voltage, the other two phases would be at half that, but negative voltage ? Therefore it’s all balanced so you don’t need anymore cables.
If that’s correct then this is where I become stuck.
Then from that transformer a single phase comes to a house. We need a complete circuit in the house so we introduce a neutral at the transformer (is this the basis of a star connection) off of this main neutral cable in the road we attach a main neutral that can come into the house ? (not including anything to do with earths or cpcs )
Reactions: Avo Mk8
1:35 of the video below kind of visualizes your rope theory!
As @Avo Mk8 says power = current x voltage and as I & V both reverse each cycle of AC then the power is flowing in the same direction. Also while the L & N have equal but opposite I, they also have opposite V (depending on where you reference it) so power flows in the same direction.
Now you might argue if it is 230V & 0V then all power is in the L, which is reasonable enough, but if centre-tapped (as the typical 110V yellow supplies on building sites do for safety, so 55V-0V-55V) then you have half power on one, half on the other. But however you chose to reference 0V you get the same total power for L+N, so the definition of N as 0V (give or take a volt or so drop along the cable) taking power as in the L is adequate..
Yes, typically in the UK the HV feed to a substation has only 3 line conductors, L1, L2, and L3 from a 3-phase supply. The primary windings are normally delta-connected to these 3 line feeds. Dropping N saves a 4th conductor which is a significant cost and as you say, is not actually needed here!
At the sending end (generator, or maybe a higher-voltage substation) then there is a neutral point for the 3-phase that is earthed so all lines are at known potentials w.r.t. the true Earth. A complication in the HV world is often there is an added impedance in the N earthing designed to limit the magnitude of any fault current to a value that is easier to handle, while the protection relay ponders if the fault is temporary or needs disconnection.
Yes, at the secondary (LV side) in the UK it is almost always a star-connection with the centre point the N which is then earthed via some arrangement of earth electrodes.
To save on cable, it is now common to have a combined N & E in the main cable (protective earth neutral = PEN), and multiple earth electrodes attached along its length (sometimes the lead sheath of old cables that have been superseded but remain buried, etc) to help a little with reliability & safety (protective multiple earthing = PME). This is known as "TN-C" as N & E are common (the 'C') part. For each house the N+E is taken along with one of the L and fed to the house, at that point (usually DNO cutout) the N and E for the installation are separated out. As N and E are now separated, it becomes TN-C-S
In the past there would be separate N & E from the substation, with the E often the cable steel armour or lead anti-corrosion sheath, but for cost saving that is not usually done in public networks (where different rules apply and TN-C is permitted) but it the usual way with private substations where the usual wiring regs apply that prohibit TN-C for safety reasons.
And yes, the safety aspect of an open PEN is a real issue today and has been forced back in to debate with electric cars being attached to that network and folks likely washing them, etc!
Okay I’m feeling like I’ve got abit more knowledge than yesterday now, but I have another question now ?
So during the negative portion of the sine wave, voltage is moving from the neutral through the load to the line ? If this is the case would you get an electric shock from touching a neutral ? For example if you turn the MCB off to do maintenance to a socket. The socket is safely isolated but if it’s still in the neutral bar and the current is alternating into the bar wouldn’t there be a risk of electric shock ?
Almost there but still not quite.
Rather than thinking of the negative half of the sine wave as 'putting voltage on the neutral', what actually happens is that voltage is still on the active wire, but now it's negative to earth reference rather than positive. The neutral stays at 0V as it's bonded to earth reference.
Thankyou for your response Electrochem, is there any other way to explain this as it’s gone over my head abit,
Thankyou
Think of the basic generator you described at the beginning of your previous thread, except it is now generating 230V. You connect one wire to an earth stake and also to one connection of a light bulb. The other generator wire connects to the other bulb connection (call that 'live'). This somewhat mimics power coming into a house.
You are standing on the earth. You touch the wire that is connected to earth. Why would you get a shock?
This is what is happening on the 'live' wire - does this help?
(PS I may have confused things with a red line - that's just supposed to represent the zero volt axis of the 'live' waveform)
I think so. So the generator in a simple form has a large magnet in the middle rotating, creating a push pull (voltage) positive negative force.
Three phases leave the generator and end up at a step down transformer that steps it down to 230V. Up until this point no neutral is needed as the three phases balance each other out ?
Now,
At this point, in the centre of a star connection transformer we introduce a neutral. From a single phase we connect this to a property. As this property is single phase we need use a neutral which connects back to the neutral in the road which is connected back at the centre of the star connection.
What I am struggling to grasp still is why the electricity upto this transformer is alternating.
But then when it comes into the house only the line side is live.
Using the second diagram of the transformer I’m struggling to understand why if I grabbed hold of the neutral I wouldn’t get a shock as by an alternating current concept for half the time the current is flowing through this cable.
The only way I can make this make sense in my head at the moment is - If I’m holding the neutral. The current is attempting to flow through me through the ground and back to the transformer. And because the neutral is connected to the earth. I am effectively at the same potential difference to the ground i.e, if the neutral cable Im holding is either pushing or pulling the electrons, because I am connected to the ground, which is connected back to the neutral. There can be no push or pull effect because, back at the transformer neutral and ground will always be the same charge either positive or negative, so there is no electron flow.
I sort of think I have explained to myself my conundrum I initially posted but I’m posting this anyway to see if I can get some confirmation from you guys.
Thankyou in advance
I think you are getting confused between the voltage on a conductor, and current flowing through it, or the relative dangers thereof?
It doesn't matter whether we talk about AC or DC. Your concern relates to what happens when you connect one side of the electricity supply to ground/ earth/ 0V/ and you.
With one side of the supply grounded (eg Neutral) there is a DC or AC voltage on the other supply wire (as illustrated by the sine wave I posted)
The fact there is current going through the neutral, many Amps or whatever, won't give you a shock. The neutral is at the same potential as you. Even if an AC supply, it's not alternating, it is at zero potential all the time (before considering the real world of resistance of cables and connections). It's the live wire that's wanging up and down in voltage, but not the neutral - it can't - it's tied to ground/0V!
Yes
The pushing and pulling of electrons is all about current. There will be/ can be current. You not getting a shock is all about voltage. There is no voltage on the Neutral.
Thankyou in advance
We don't mind if you keep asking if you don't understand. And I'm sorry if my attempts to explain don't resonate with you - I'm sure someone will be along to help!
Yes
Right I think Im getting there, so current flow is happening throughout. However in a simple analogy the pushing and pulling action (voltage) is only pushing and pulling on one side (The phase/ line conductor side). So current flows back and forth throughout the circuit from the generator through the transformers into a domestic dwelling/ installation and then all the way back.
Neutral and Earth are bonded/ linked together at the same point in the centre of the star connection transformer. So if I was to touch a neutral, (stay with this bit) I’ve almost got an imaginary cable attached to my feet which runs back underground to the transformer, but this is linked at the same point the neutral is linked at. This imaginary cable being a route through the earth. Because I’m creating a circuit that back at the transformer end isn’t linked at two seperate points/ opposite ends of the transformer there is no potential difference as there can be no push or pull effect of electrons. Therefore no electric shock.
Where as if I am touching the phase wire I am completing a circuit from the phase through the earth which attaches to the opposite end of the transformer winding.
Since the phase side is connected to the opposite end of the neutral/earth there is a potential difference and work can now be done. I.e. the electrons can move back and forth - therefore electric shock/ electron flow
Yes the voltage (tension) is only on the live side as it were. The pulling and pushing distance moved was the current. Both ends of the rope move the same. The current in L and N are the same.
yes
Yes. The ground is a conductor, so your imaginary cable is 'real', but with some resistance (sorry thats probably a complication!)
I think I follow, yes. I find it easier to think in terms of current flow - just call it current - rather than worrying about electrons pushing or pulling.
Yes
yes
Yes
Thankyou very much for all the help, I’m sure there’s lots more to learn but I do feel like I understand the answer to the question I initially asked.
So that all being said the phase conductor comes from the transformer to the installation and the neutral goes back to the transformer to the centre.
Back at the transformer on the opposite side of the windings we have the side of the transformer which goes back to the generator. (Let’s keep it simple and say there is only generator - transformer - installation). On the generator side of the transformer or back at the generator. What is the determining factor as to why it’s the tips of the star connection where our phase wire connects that carry the voltage ?
I would have expected back at an AC generator for a single phase to be connected in the generator at 180 degrees ?
What I’m asking is back at the generator which side is our voltage being produced on to then attach to the phase cables ?
I feel the answer is because of the neutral introduction, or to do with the way delta and star are connected ?
Just had a look at some animations of a star and delta connection. Think I was getting slightly confused.
Taking mention back to previous early comments. All the phases work together because they are balanced as they leave the generator and then I’m guessing on one side of the transformer we have a delta connection and on the other side is a star connection. In this portion is where we get our phase conductor at the top which gives us the voltage transfer ?
Firstly, power distribution is not my thing, I'm not the best person to advise.
Conceptually you summary is fine. All phases are typically held at about the same voltage, via an earthing transformer or similar at the generator. And as you say, the generator can provide a balanced feed to a delta to star transformer to step down the voltage and provide the star tap.
In this portion is where we get our phase conductor at the top which gives us the voltage.
But it’s we get from one side to the other Im not sure about. Is that correct ?
Not sure what your asking here, but at the star outputs of the transformer you have the three live phases (don't touch!), and their star neutral point that is connected to ground (can touch!). So you could feed three households, one from each phase, and a neutral return to each. And in the unlikely event all three households are using exactly the same amount of electricity, eg the same current, (a balanced load), that current will be flowing in the neutral wires back to the transformer, and where the neutrals all connect together, their currents sum to zero. So for balanced household loads, the star neutral point of the transformer wouldn't carry any current. Mind blown. Of course that's an idealised situation.
Thankyou very much for your help truly. Dis regard that last section I was looking at a picture of delta and star connection diagrams and taking them far to literal. I drew a Y inside an equilateral triangle to look how it would work and did a bit more reading to see how the coils actually wind around next to each other to create the contacts.
I feel like I’m there or there abouts.
Lastly I gather at a generator the ends of the cables are connected together in a Delta fashion. Then if we follow these three cables all the way over the plyons through the system eventually we get to a transformer which steps it down. We have a star or Delta connection one side and star on the other. Then from the star supply side, our phases then feed say a road of houses, and each of these houses taps onto the neutral to allow for single phase ?
If this is correct Thankyou very much for the help over the weekend. I’ve Definatley got a lot more knowledge than I started with on Friday.
Absolutely. All get the neutral and a phase. Blocks of flats and commercial buildings tend to get all 3-phases (and the neutral obviously), phases shared out within the building to balance the load where practicable. My previous house actually had a 3-phase supply to the fuse head, but just a single phase was connected to the meter.
Best wishes for a future in Electrics. Keep the faith!
Reactions: Rob678
Thanks again, I’m sure I’ll be back with many more questions
Hampshire
Trainee Electrician
Current flow in neutral but no voltage ?
Rob678,
Rob678,