Why? Because although at 30m it is far enough away from the house and (probably) any extraneous metal, with a TT I have a separate earthing system which is, if you like, under known control conditions and not subject to problems at the suppliers end. TT'ing I agree is not really an issue where step-voltages are highly unlikely but I generally will always TT an outbuilding combined with 30mA RCD.
Sorry, above should say "Exporting PME....."
Then you're a fool!! So what happens when that 30mA RCD fails then?? You've been listening to far too many scaremongers!!
All things are liable to fail. But I do not get in my van and think, better not drive today because the brakes might fail. If everything is designed correctly and works as it should then I should not be having sleepless nights about possibilities of failing components. Once my test & inspection cert. is done (and BTW, I always take photographic evidence of my installs :smiley2:) then the installation is as it is and so long as i can stand up in court and prove everything was done within regs. then I am happy - even if I might agree with the view "in hindsight.....":wink5:
In other words Sod the customer you've taken money from!! Magic!!
Any electrician that's fool enough to ditch a perfectly good TN Earth in favour of anything like the totally unreliable recommendations of BS 7671 regarding TT systems, needs Certifying!!
Along with the install!
All my TT installations have been perfectly good too! :grin:
But you have installed a 10mm 3c SWA so the third core is of sufficient CSA to double as a cpc and main bonding!!
Question--If you were installing external lighting not attatched to the main house but fed from it would you treat the lights as 'outbuildings' and TT them or use the house earthing system?
Edit....To be fair you have not stated the PME cant be 'exported'....but that you prefer not to.I'd have to disagree but thats your choice.
You may as well TT the house using that argument.
TT or PME, it complies with BS7671 and it is up to him as the installer. Sometimes TT is preferable over PME is bonding is required at sub main. I do either dependant on situation. It is not a case of one size fits all.
Thinking about it, in the summer I connected power to a DB in a brick built shed (about 5 metres from main house. Customer supplied all materials and I had to take the power source from an existing outside socket (customers preference). 3 core SWA provided so armour and copper core all earthed back to same (PME) earth point. No problem with that from my point of view but when supplying out buildings from which a person is stepping in, and out, potentially hanging on to something live, then my preferred, and standard procedure, is two core (cheaper) SWA, TT earth, and 30mA RCD fed from non-RCD MCB.
Very true, but if you read his posts here again, ....Not for this guy!!